    Toshiba vrf h01 fault



    Anybody ever had a h01 fault (compressor breakdown) that you could share any info ?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba vrf h01 fault

    tosh super multi r407c -3 pipe- were a f**ker for comp failures- 2 compressors on 1 shell, weighed about 80kg- took 4 hrs to remove electrics-boards etc-then undo the reactor on top then split the acoustic enclosure.
    then u see the 1 3/8 common suction silver soldered onto the steel comp stubb-at 12 inch high-
    had 3 comp changes 10r ago-

  3. #3
    Join Date
    Jul 2009
    Location
    stoke on trent
    Posts
    48
    Rep Power
    0

    Re: Toshiba vrf h01 fault

    Its a 410a super multi mmy-map 1002fte

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Toshiba vrf h01 fault

    You can download the full manual HERE.

    If you look on pg 91 you will find the flowchart for troubleshooting H01.

    But generally, the second code will tell you which compressor tripped and then it's just basic faultfinding.
    Does the windings have the right resistance?
    Is the compressor down to earth?
    Is the inverter's output OK?

    Happy hunting!



    .
    Last edited by The Viking; 12-04-2012 at 12:37 AM.

  5. #5
    Join Date
    Jul 2009
    Location
    stoke on trent
    Posts
    48
    Rep Power
    0

    Smile Re: Toshiba vrf h01 fault

    The outcome was, compressor 2 was faulty even though it metered out ok, not down to earth and inverter output ok. Replaced compressor, all up and running now.

  6. #6
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Toshiba vrf h01 fault

    The job is not complete until you diagnose the cause of failure of the compressor or you may have another service call soon.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba vrf h01 fault

    metered out ok-multimeter the windings or insulation test? could have been siezing up to cause the problem-have u done an acid test on the oil?