    Re: Using two glycol storage tanks in a cooling circuit ? Please help

    Best give you a non real world example

    Imagine;
    All mixing in the save tank and same flow to process and chiller
    you want 5C going to the process
    10C is coming back from the process
    Therefore
    5C must be entering the chiller
    0C must be leaving the chiller.
    The chiller saturated suction temp (SST) would be -5C.

    Let then presume we a have twin tanks .
    The 10C from the process effectively goes into the chiller. and 5C leaving the chiller and going to the process.
    All things being equal, the new SST would 0C
    the chiller .
    the increased SST would give approx 20% more net refrigeration, for very little increase in power use.
    So your COP could go from say 3.5 upto 4. So around a 6% saving in power.
    Of course this will change depending upon refrigerant, compressor type and working conditions (pressures, flows, temps)

  2. #2
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    66
    Posts
    78
    Rep Power
    21

    Re: Using two glycol storage tanks in a cooling circuit ? Please help

    boost you are giving him a good thinking.

    I would go for all glycol coming back direct to the chillers, this will improve the exchange in the chiller as boost is telling you.
    Use another chiller to keep the buffer on correct temp.
    If the chillers can not keep up, then use the buffer tanks.
    In the night use two chillers to cool down the buffer for the day time.