Thread: carrier 30 rb
06-05-2012, 03:36 PM #1
carrier 30 rb
fault p-32 p-33
water pump fault ,i bridged input but still have this fault alarm .
any ideas?except for replacing card!
06-05-2012, 04:00 PM #2
Re: carrier 30 rb
Cooler Pump Fault
P.32 Pump 1 Fault
P.33 Pump 2 Fault
Criteria for Trip
The criterion is tested whether the units are
ON or OFF. This alarm will be generated if the cooler pump
interlock opens. When starting the pump, the control must read
an open circuit for 3 consecutive reads. If the pump is operating
and the circuit opens, the alarm will be generated immediately.
Action to be Taken
The pump and machine will be shut
down. If there is another pump available, the control will start
that pump, restart the machine and clear the alarm. If no other
pump is available, the unit will remain OFF.
Reset Method
Manual.
Possible Causes
If this condition is encountered, check the
following items:
Check the interlock wiring circuit.
Check for a control signal to the pump controller.
Check the cooler pump contactor for proper operation.
Check control voltage for proper voltage. On 208-volt
systems, be sure the proper tap on TRAN1 is utilized.
06-05-2012, 04:04 PM #3
Re: carrier 30 rb
Hi IM
THX CHECKED ALL THAT ,ILL BE ON SITE AND CHECK AGAIN.THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
06-05-2012, 04:17 PM #4
Re: carrier 30 rb
https://rapidshare.com/files/2878700323/30rb-4t.pdf;
30rb manual- incase you havent got it
07-05-2012, 02:41 PM #5
Re: carrier 30 rb
turns out its the flowswitch!
they both sit on the same alarm !!!!p32-33
no seperate alarm for the flow!
i was wondering, this electronic flowswitch sends a signal via a resistor to a discreet input(ch15b) .
could this input be bridged??
thx for responseTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
Dear Josip, Many thanks for your explanation. I do not understand what you mean by "Economizer vessel"? Can you elaborate? What I understand from your explanation is : when capacity is...
Screw Compressor Eco & Liquid...