    pressure testing with manifolds with sight glasses
    Does anyone still use manifolds with sight glasses? I use to as it was the way i was taught as an apprentice. Now ive had a lot more experience ive moved away from using ones with sight glasses and only use ones without sight glasses.
    Javac have designed a new pressure and vacuum manifold called a PVR has anyone had one or used one im interested but could need some one elses view if they have used one?
    Feb 2008
    505
    Re: pressure testing with manifolds with sight glasses
    i use a single manifold without sight glass
    3,856
    I have a single gauge Refco one for pressure testing, then swap over to my normal manifold for commisioning.
    Looks similar to this,
    http://elanmax.com/?cat=91
    Apr 2008
    Southampton, England
    49
    1,023
    I do the same as MS there, an R410A Refco high side single manifold unit. Very handy too that you can connect to both sides of the system (if access ports allow it anyway) with one gauge so no need to worry that the system hasn't equalised.
    If truth be told though, still the odd test with my normal gauges.
    Cheers,
    Andy.
    Dec 2011
    Australia
    13
    MS . Wouldnt u pressure test with high side single gauge . as the low side on wouldn't go high enough ? is this just a picture and you couldnt find a red one ?
    For 6 years i have used gauges with no sight glass . i bought gauges the other day and they happen to have a sight glass.
    What do i do with it other they looking a pretty bubbles ?
    I just look at the sight glass of the unit.
    DO the manifold ones have much purpose ?
    3,856
    Quote Originally Posted by Simeonx1 View Post
    Yeah thats the only picture i could find, i have one with a high side gauge on it.
    Jun 2010
    Wales
    Yeah we only pressure test with a single high side gauge, as a few years back one engineer had a incident when a few weeks prior had his sight glass/ seal replaced by a wholesaler and then he was pressure testing a 410a split and the sight glass actually blew and lodged into his hand!...
    Feb 2012
    5
    I'll have a look at the refco single manifold then guys.
    The pvr has a vacuum gauge on the same manifold block with the pressure gauge and set points so I'll have a look in to that too. It's always safety with me so whichever looks safest that's wot I'll go for
    Jun 2009
    VA
    64
    3
    Do you usually pressure test a R22 system after fixing a leak or do you just vacuum then service? Thanks.
    3,856
    Quote Originally Posted by Fishin View Post
    Would depend on where the leak was and what was done to repair it and also the type of system.
    Give an example.
    11,025
    Would normally expect any system that had a leak repaired to have the repair tested.
    Jun 2009
    VA
    64
    3
    The tee going to the TXV was leaking. Replaced tee by brazing , vacuumed then serviced with R22.
    Oct 2006
    1,843
    Where we are the requirement is IF you do a new install or fit a major component,
    you are required to prove the strength of the new part / install.
    Changing a condenser, compressor, oil seperator or evap could be deemed a major component,
    changing a filter core dryer or TEV orrifice maybe not.
    You need to ask your self how did you prove the brazed joint was gas tight?
    You do not always have to do a strength test but a leak test / gas tightness test
    might but considdered the correct thing to do?
    You can't use a vac as a pressure test. the pressure is too low and in the wrong
    direction.
    All the best
    taz
    Jun 2009
    VA
    64
    3
    Got ya. Thanks.
    Mar 2007
    manchester
    63
    always nitro up after any repair- why not???????
    May 2010
    Finland
    44
    9
    I use only Refco, Ite etc. manifold's with sight glass and I dont have any problem's. Pressure testing I use nitrogen gas (N2).
    dannyboi88's Avatar
    dannyboi88 Guest
    Quote Originally Posted by paddyaircon View Post
    With you on this one, just puts the mind at ease to know iv done a test on it.
    Aug 2010
    110
    14
    How far into vacuum did you go? What are the regulations where you are? Where is VA?
    Mar 2007
    manchester
    63
    i know guys who just still purge lol -