    Donaldson ultracool malfunction codes



    Hey every body,

    does any one have a list of th malfunction codes of Donaldson chiller units???

    Our chiller unit show an alarm (EL1). There is no description of this alarm in the manual!

    I have contacted Donaldson but they told they are not responsible for the service any more.

    Can someone help?



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Donaldson ultracool malfunction codes

    i would try hvac-talk as it's an american made unit and that's an american based forum

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Donaldson ultracool malfunction codes

    Hi Jebril.
    It may be worth contacting Lauda on the below address as they took over (Purchased) certain models
    in 2007.
    info@lauda-ultracool.com

    Grizzly

  4. #4
    jebril's Avatar
    jebril Guest

    Re: Donaldson ultracool malfunction codes

    I already contacted Lauda on 10/04/2012 but nobody answered me. sent another mail on 26/04 and still waiting...

    other ideas??

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Donaldson ultracool malfunction codes

    As far as I can remember "all" E faults on these units are thermostat or thermistor faults
    EL1 ?? Which is low supply voltage ,I think.

    Top of page 38

    https://docs.google.com/viewer?a=v&q...lnqHp_axjsZWdA




    Cheers
    Stu
    Last edited by stufus; 29-04-2012 at 08:57 PM. Reason: remembered something else
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    jebril's Avatar
    jebril Guest

    Re: Donaldson ultracool malfunction codes

    Thank you for your quick replying stu,
    it was helpful to know why this warning message come. but we checked several times the input voltage of the chiller and we measure 460 VAC on all phases.
    (To be exact: L1, L2 : 456V
    L1, L3 : 456
    and L2, L3 : 460 ). I don't know if this make a trouble. But yesterday we bought a voltage stabilizer to make sure that the input voltage to the chiller and machine is stable. After we tried ... the warning is still flashing !!!!! I'm now really desperate.

    Engineers .... please help me it shouldn't be so hard. because in the manual it says that the problem is related to the power supply!

    regards

  7. #7
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Donaldson ultracool malfunction codes

    Have you done the old trick of powering the unit down for 5 minutes...

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Donaldson ultracool malfunction codes

    Next port of call would be all neutrals on the control circuits.
    Prime suspect's for pulling control voltage down would in my opinion be a solenoid coil and/or a traffo.
    But work through all connections.
    Cheers
    Stu