How to calculate the required flow rate from the total refrigeration capacity is 152720 kilocalories per hour (kcal/h)?
You have to respect the circulation rate informed by the manufacturer of the plates.
You should check manufacturer’s literature or read older posts on this topic like:
http://www.refrigeration-engineer.co...p/t-13313.html
Now as to the math with no assurance these are correct numbers, look at it this way:
In one hour you need to extract 152720 kcal and to do that you must circulate 132 litres per 1000 Kcal then you have to circulate (152720 x 132)/1000 = 20159 litres.