    I have recently received a Beverage Air MT72 three door reach-in refrigerator that is about 10 years old. We will be using it on our farm to keep fresh eggs cool but not cold.

    I am trying to determine if the temp control is working properly. If the temp control is set on a lower setting such as number 1, it will cycle the compressor on when the air temp in the box is 14.4*C (58*F) and off when the box air temp is 4.4*C (40*F). This seems like a large swing in box temp. Is this normal or do I have a problem with the temp controller?

    Thank you.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Temp control on reach-in cooler

    You need some kind of thermometer to see the temp, then you can adjust it.

  3. #3
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Temp control on reach-in cooler

    And it depends on whether the thermostat is reading cabinet air temperature, or evaporator temperature, as some brands of 2, 3 and 4 door coolers do here.
    Product temperature will not follow air temperature that quickly, so your average product temperature will be around 49 degrees F, or about 9 degrees C.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  4. #4
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Temp control on reach-in cooler

    Thank you both for your responses -

    The unit does have a thermometer installed and I have also placed a second one in the cabinet temporarily to confirm the installed one is reading accurately. Both are giving me the readings I posted.

    I have not pulled the cover off the evaporator to see whether the temp control cap tube is set to read air temp or evap temp.

    So, do these swings in air temp seem correct for this type of unit?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Temp control on reach-in cooler

    Place a bowl or bucket of water in the fridge and then use the water temperature to determine the thermostat settings.

    It's no good measuring air temperatures...you need the product temperature.

    IIRC the ideal temp for egg storage is +10C.

  6. #6
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Temp control on reach-in cooler

    Quote Originally Posted by frank View Post
    Place a bowl or bucket of water in the fridge and then use the water temperature to determine the thermostat settings.

    It's no good measuring air temperatures...you need the product temperature.

    IIRC the ideal temp for egg storage is +10C.

    Thanks frank that is a good suggestion to take temp from a bowl of water. Yes, we were hoping the cooler would be able to keep the eggs in that temp range.