Thread: Carrier 30gx

  1. #1
    andymackay1979's Avatar
    andymackay1979 Guest

    Carrier 30gx



    Im having trouble with above chiller tripping on low sst, currently it will pump into vacuum on start up and trip out on same fault or ecconamizer transducer. Any help would be greatly appreciated.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Carrier 30gx

    hi andy , it lookes like < with the cold ambiant < that the suction psig is tripping the L-P< sst ? to get round this fit a < winter start pack< so as to bypass the L-P untill the unit gets warmed up , good luck, = sedgy,

  3. #3
    andymackay1979's Avatar
    andymackay1979 Guest

    Re: Carrier 30gx

    Hi sedgy, other circuits & chiller on site are working ok, I'm thinking along the lines that due to low load on this particular machine that there is oil logging causing pump down on the expansion valve. Checked stepper motor (ok)

    What do u think?

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carrier 30gx

    Hi
    check your econimiser sensor and solonoied.
    i have had problems with these buggers.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Carrier 30gx

    hi andy,
    another tip < on carrier units < is the long very small diamiter pipes going to the gauges, have had to replace a few over the years , it seamed the pressure drop effected the gauges, wether it was a blockage or just the small size cannot remember < it was 200 years ago < lol=sedgy

  6. #6
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier 30gx

    There is no LP or gauges fitted to this chiller, seems you have a problem with your EXV if its pumping down into a vacuum.

  7. #7
    andymackay1979's Avatar
    andymackay1979 Guest

    Re: Carrier 30gx

    Thanks for the feedback, the plan of action is to return on a warmer day and build up the water temp so we can run this circuit under a higher load for an hour or more... Hopefully this will return most of the oil to the seperator.

    This machine runs as backup to another chiller therefor has v low load most days through the cooler periods (wich is most days in this country) so I think the exv/cooler is oil logged and causing pump down, after a period of time this settles and we are able to run the circuit with no issues until it cycles off and back on again then it pumps down... It had a new exv recently fitted by another engineer so we know the valve is ok I have also checked the valve operation (ok)

    We have recommended to the client to change the control strategy so that the chillers change over and this chiller can run as lead on a changeover basis.

    This is just my trail of thought on the problem, if anyone has had a lot of experience with this issue it would interesting to hear your thoughts too
    (the machine is a 30gx runs on 134a approx age 2005 no data plate)

    Cheers. Andy.

  8. #8
    Join Date
    Mar 2008
    Location
    United Kingdom
    Age
    54
    Posts
    35
    Rep Power
    0

    Re: Carrier 30gx

    Hi, the first thing to check for on these units is the EEV connection that screws onto the EEV. These were badly insulated which resulted in chronic corrossion, I have had at least ten changed already. When fitting a new one use silicone grease on the plug, and not too much, and insulate the plug nicely with armaflex tape. I have also had dodgy economiser tranducers go on me.
    Good luck

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carrier 30gx

    Hi
    good advice from burrah boy.
    couldnt agree more!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  10. #10
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Carrier 30gx

    I would say: ***** shortage.

  11. #11
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: Carrier 30gx

    would say check charge but if it cycles fine all the other time it seems fine going out on sst is an indicator of that had the plate prob myself if you open up the pannels behind the mains isolater they usually have to unit model carrier can then tell you system charge from that or you can download a manual for it or request one on here you might get lucky i had 3 large carrier dual circuit chillers next to each other only 4 yrs old not one had the correct charge in and 3kgs below plate charge is enough to cause problems dont do as carrier recommend and add refrigerant in 3kg bursts reclaim and recharge then you know for certain change drier core as well its never a bad idea sorry if i teaching you to suck eggs good luck with that one
    I can fix broke but I cant fix stupid :)

  12. #12
    Join Date
    May 2012
    Location
    france
    Age
    48
    Posts
    1
    Rep Power
    0

    Re: Carrier 30gx

    i everybody i am french chiller and work on these machine.
    i dont speak very well english but i am going try to help you.
    there is 5 possibilities:
    Low charge of ***** r134a.Control the charge at 100% running if you can: Condensing t°-Liquide line T°=approx 7°/8°C
    Pb with EXV on liquide ligne.control the EXV connexion or control it with the pro dialog +
    there is too much oil in the evaporator:control the pinch LWT-SST
    Control the difference between the T° sensor and a gauge(manometre) when the machine is stopped
    Control the delta pressure of the drier filter IN/OUT.

    Tell me if understand and sorry for the mistake.

  13. #13
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    Hi i have problems on this machine 30GX102 with pro dialouge plus controller, 51 kg in each circuit. It keeps nuisance tripping on Alarm 62 and when an engineer attends-resets, it runs away quite happily, quite annoying. Any ideas? Compressor filter, pre-filter, pump and oil all replaced. one strange thing was no oil was removed however pump was leaking from the body so have assumed the oil has escaped. I suspect a transducer issue or board, not too used to these machines so would appreciate any input in further diagnostics.

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Carrier 30gx

    Hi Wilko.
    You don't say whether you have a description of that alarm code?

    So below may help?

    I would also look for any indirect influances that could give oil issues.
    Grizzly
    Last edited by Grizzly; 24-05-2012 at 10:36 PM.

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Carrier 30gx


  16. #16
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    Quote Originally Posted by Grizzly View Post
    Hi Wilko.
    You don't say whether you have a description of that alarm code?

    So below may help?

    I would also look for any indirect influances that could give oil issues.
    Grizzly
    hello grizzly, where did you get this alarm description, the book im reffering to states high oil differntial alarm which has had me checking all sorts of other things..... We have a 30GX102 Chiller with the pro-dialogue grey screen. 2005
    Were having alarm 62 appear for oil differential pressure which I thought today was due to the non-functioning oil separator heater, but also the oil differential transducer, when checking difference between discharge pressure and oil pressure the differential oil pressure seemed to be much higher, where is this oil differential transducer?

    We have also changed oil, comp filter, pre-filter and pump.

    What regulates the temperature control wise (oil heaters)?I noticed the heaters were off including the pipeline heater, when the pipework was pretty cool well below 40deg C, I found the separator heater open circuit but that does not explain why the pipeline heater was not on. The oil level switch contact was closed on the input option 9 so im scratching head a little,

    Ever known the input board to fail? Or know what else would cause the control relays (contactors- 24vac coils for the heaters) not to be energised other than being satisfied on temperature?

    Hopefully your world of wisdom can help me out of this pickle…

  17. #17
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    hi again grizzly, just to add to that, the pre-lube is fine, it gets going but cuts out once it has been running a short period, since my involvement this has been multiple times but because the water temp is high, once its lower and the approach is about 4-5 deg it copes sweet as, in fact it does not trip out, then gts down to 1 deg C.

  18. #18
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    Quote Originally Posted by install monkey View Post
    hello install monkey- thanks for manual, i have this... it does not represent the correct controller, and the book i have states alarm 62 is for

    62 Max. oil pressure difference,compressor A1(Discharge pressure - oilpressure) >340 kPa for morethan 6 secondsCompressor A1 shut down Manual Obstructed oil filter, oil solenoid orshut-off valve blocked, or manual
    oil valve closed

  19. #19
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    Hello French Chiller- Have you got any idea? my post below.....

  20. #20
    Join Date
    Apr 2012
    Location
    u.a.e
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: Carrier 30gx

    hi dear ,i have a carrier 30gx french chiller pro dialoge plus chiller and i have problem in this is low suction saturation temp and the alarm code is 56 & 57 , ihave tried to top up freeon r134a, ihave replaced filter drier, and i have increased the water flow , i have replaced mother board and i increased the condensing temperature from 37c to 41c and still the same problem. can anyone help me . thanks in advanced

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Carrier 30gx

    stepper motor on the txv or the lead to it can get moisture in- weigh out ur gas to see if its correctly charged as per nameplate!

  22. #22
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Carrier 30gx

    still got alarm 62 coming up....having nightmare with this inconsistent nuisance alarm... new oil charge, new filters, full charge, any ideas?

  23. #23
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Carrier 30gx

    had this problem turned out to be a piece of oil pump in the oil line at the compressor end.

  24. #24
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: Carrier 30gx

    why does no one ever give a system log? everyone has to guess! frenchy gave some good advice.