    has anyone had intermitant oil problems with one of these chillers.
    one compressor runs ok but number two will be working ok sometimes when i go to site but other times it trips on oil failure with no oil pressure at all just vapour at the schrader on the oil pump,the oil level is ok and the crankcase heater is working so there is no liquid in the compressor.
    Oct 2007
    manchester
    5,639
    45
    Re: york ycaj oil problems
    have you tried draining the oil and inspecting the oil pickup filter gauze,also any swarf or crap in the sump?
    ireland
    1,451
    41
    What model YCAJ? some j or h compressors had faulty oil pumps and oil sensors.
    al
    Oct 2009
    77
    243
    ycaj765t9gsi, the compressor is a jl632q5046sy, do you know if there is a nrv in the oil line between the sump and the oil pump.
    Somerset
    69
    4,712
    I would go with IM's diagnosis.
    Feb 2012
    Bolivia
    270
    14
    If you already checked Install Monkeys suggestion and is OK, measure both crankcase pressures while the compressors are running, with the same gage. Do not use different sensors unless you have just calibrated them.
    Somerset
    69
    4,712
    Quote Originally Posted by aramis View Post
    You got me there aramis.
    If there is no oil pressure how do you propose to run the compressor?
    Oil pressure displayed is a calculation of actual oil pressure and suction pressure ( crankcase pressure).
    Maybe that question is unfair as if the strainer is checked / cleaned there would be fresh oil in the compressor upon start-up. Therefore initially there would be no oil pressure problem.
    The Oil pressure is not there on start-up rather than fading whilst running, or so that's the way I read redroges question/ dilemma.
    The difference is huge because there are many things not part of the oil circuit that will affect oil pressure issues in any recip.
    So if the pump is being starved on start-up. As has been suggested the oil pump pick-up strainer would be a good place to start.
    As to why you would check the crankcase pressure you have me there?
    Oct 2009
    77
    243
    i think the answer is get gasket set and start stripping it down
    cheers lads.
    Oct 2009
    77
    243
    Been back today found the compressor running sweet as a nut with oil pressure of five bar,can,t see it being a strainer blockage!
    Somerset
    69
    4,712
    Could of been High oil temp, which in turn causes the viscosity of the oil to drop and it's pressure with it.
    Once it's all cooled down,all is sweet until the next time.
    Oct 2009
    77
    243
    When it was tripping there was only vapour at the oil pump.
    Somerset
    69
    4,712
    You got me there my friend?
    J's will throw oil for a pastime is running on part load for long enough.
    Did you top it up to get it away?
    It's possible to get vapour whilst at a standstill.
    What's the suction pressure doing and the oil temp?
    Somerset
    69
    4,712
    Hi redroge.
    Just a thought sometime a oil pressure fault is the first cutout reached.
    Ie when suction pressure drops to low the software sees it as low oil pressure.
    Especially if the lwt probe is reading high.
    So low oil is not always the problem.
    Oct 2009
    77
    243
    Just recieved some info from york does anyone know what an oil educator is as i,ve never heard of it before.
    ireland
    1,451
    41
    I think it's the pipe that collects oil from the suction chamber where the windings are, brings the oil to the oil sump proper.
    al
    Sep 2009
    Cyprus
    64
    110
    15
    Redroge when you go again to check the compressor i need only one thing to tell me and if you still having trouble i know the solution. i need to tell me the compressor discharge end temperature and especially the one in the continuously loaded cylinders
    Oct 2009
    77
    243
    Compressor is still running ok.
    Sep 2009
    Cyprus
    64
    110
    15
    ok redroge good to know that the compressor is running ok if you get that problem again just let me know