    Blocked coil



    Hi all I have a Trane chiller unit ECG900 that is totally wrong for application. The coils are undersized and the fin spacing far close together. The site is a papermill and the coils have got blocked solid with a mixture of paper dust and glue we have tried cleaning the coils but cleaner won't penetrate the coil. Having HP problems now and need a specialist coil cleaning company to come have a look any recommendations we are in Manchester Uk



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Blocked coil

    new coils from trane and then fit insect screen to resist the crap in the air-or filtter media to cover the coils
    try a steamer them ones they use to clean the grout between tiles (not wall paper one) polti do em-other are available- to try and blast the crap clear- as you cant do hot works in a paper mill.
    Last edited by install monkey; 21-04-2012 at 03:49 PM.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Blocked coil

    Was talking to the guy from Advanced engineering at a recent open day, he said they will visit a site to help select or make a new coil cleaner chemical to solve specific problems, would be worth giving them a call,

    http://www.advancedengineering.co.uk/products/
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Blocked coil

    I'll agree with Install Monkey on this one regarding the steamer ,had a similar problem in a factory that made high density fiber board similar to MDF.
    Nicked the missus H2O mop thingy and it worked a treat ,down side was I had to buy her another one as I decided to keep the first one in the van permanently.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  5. #5
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Blocked coil

    Nothing better than steel wire and patience! ... and perhaps a solvent for the glue.

    Also consider using a remote condenser.

    Finn spacing only buys you time. If the glue is sticky or the paper wet it will get covered anyway unless you wash it frequently enough, with the correct solvent.