    Getting code A03 on Carrier 40x when using electric stand-by



    This is my first post. I have a carrier 40x unit with electric stand-by, 6 years old, compressor on stand-by is 3 years old (replacement was $3000). The unit wasn't cooling so, I just had all the lines replaced and the road unit is working perfectly. The electric stand-by has an issue. I can plug it in and it will work fine for 30 or even 48 hours and then shut down, code is A03. If I try to re-start it sometimes it will start right up, other times it will buzz loudly for 30 or so seconds and shut down. I've checked my power cord and conections also checked the power and it's over 240 volts. I've also tried other outlets. and cords. The shop says it's the compressor, again. Why would the compressor work for 40 hours and be bad? Am I looking at another $3000 bill or could it be something else? I plugged it in at 12:00 pm today, and I figured I'd give it another test I set it to 0 and 8 hours later it is holding 2-4 degrees. My guess would be that sometime overnite it will shut down, or mabye tomorrow sometime. When it shuts down I have to use the road unit 1 gallon of diesel every 1.5 hours. Any ideas or advice would be greatly appreciated.



  2. #2
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    A 03…Standby / Compressor electrical motor over heat, i suggest checking the overload relay... loose wires or bad contacts inside relay.... try replacing relay before compressor...

  3. #3
    Join Date
    Apr 2012
    Location
    United States
    Age
    69
    Posts
    7
    Rep Power
    0

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    Thanks. I will try that.

  4. #4
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    Check capacitors and start relay, if its humming somtimes i would look to the start relay

  5. #5
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    what voltage is it? Is it single or three phase?

  6. #6
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    i suppose it's 3 phase, his from US...

  7. #7
    Join Date
    Apr 2012
    Location
    United States
    Age
    69
    Posts
    7
    Rep Power
    0

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    single phase.

  8. #8
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    Then moggy is right,check those as well, remove the start relay cap an see how it,s working, had one case in witch from overheating the moving element inside relay was bendt, causing it to work exactly the opposite way that it should.

  9. #9
    Join Date
    Apr 2012
    Location
    United States
    Age
    69
    Posts
    7
    Rep Power
    0

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    Great information, thanks.

  10. #10
    Join Date
    Sep 2006
    Location
    england
    Posts
    285
    Rep Power
    18

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    what happened did u fix it

  11. #11
    Join Date
    Apr 2012
    Location
    United States
    Age
    69
    Posts
    7
    Rep Power
    0

    Re: Getting code A03 on Carrier 40x when using electric stand-by

    I'm still using it on the road unit when I need to. As for the electric stand-by, I'm taking it to my refrig. mechanic, with the information I've gotten here. I don't think I can repair it myself.