    VRVIII Central Control


    Hi Guys!
    Is it possible to monitor and control VRVIII indoor units with the central remote controller without individual remote controllers? Now after setting group No. and disconnecting the individual remote controller we have "U5" error code.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,725
    Rep Power
    29

    Re: VRVIII Central Control

    When you disconnect a remote controller you must reset the power to the fan coil to stop the error message
    I'm back on the Pale

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,196
    Rep Power
    25

    Re: VRVIII Central Control

    After you disconnect the local controller(s) the indoor unit(s) it were connected to still remembers it and recognise that it is missing and throw up a fault, U5.
    To get the indoor units to forget about their old lovers, the remote(s), you will have to power each indoor unit OFF and then back ON again. When they restart they will have forgotten about the remotes but still remember their addresses.



    .

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,196
    Rep Power
    25

    Re: VRVIII Central Control

    Frank is a quicker typist than I am but at least we agree...

  5. #5
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    245
    Rep Power
    9

    Re: VRVIII Central Control

    Thank you very much!