Thread: VRVIII Central Control
-
14-04-2012, 02:30 PM #1
VRVIII Central Control
Hi Guys!
Is it possible to monitor and control VRVIII indoor units with the central remote controller without individual remote controllers? Now after setting group No. and disconnecting the individual remote controller we have "U5" error code.
-
14-04-2012, 06:42 PM #2
Re: VRVIII Central Control
When you disconnect a remote controller you must reset the power to the fan coil to stop the error message
-
14-04-2012, 06:46 PM #3
Re: VRVIII Central Control
After you disconnect the local controller(s) the indoor unit(s) it were connected to still remembers it and recognise that it is missing and throw up a fault, U5.
To get the indoor units to forget about their old lovers, the remote(s), you will have to power each indoor unit OFF and then back ON again. When they restart they will have forgotten about the remotes but still remember their addresses.

.Why not visit my website: www.the-viking.eu ?
-
14-04-2012, 06:49 PM #4
Re: VRVIII Central Control
Frank is a quicker typist than I am but at least we agree...