I found this site to be informative & I see that you can help me to understand more in refrigeration.
As I came to a site in search for solutions to improve the cooling capacity of our sytem, I find the website about the evaporative fogging system. May I know if this actually helps increase the peak cooling capacity of the refrigeration system?
I think ,here in Malaysia, has relatively low humidity as other asian country. Our existing air cooled condenser uses sprayed water as interim action (for 2years...wow). Now, its has accumulates dirts & moss all over the fins. We are trying to declogg (manually & using chemicals) the air passage but not enough. We are trying to save other condensers using other aternative condenser cooling. As for now, we cannot replace the chillers immediately so we need to find ways to put it back in action. Cooling capacity of the chillers greatly reduce & affects our process as we have encountered a lot of high discharge pressure alarm.
Any suggestion in this forum is very much welcome.
Then you should either reduce the amount of water you are spraying or improve the nozzles’ efficiency or spray further away from the fins or use it only during low humidity hours.
The idea is that water evaporates completely before touching the fins.
What you gain is dropping the air temperature form dry bulb to wet bulb. This makes no sense neither if your climate is humid nor if you use the system during high relative humidity hours.
Other problems are if the discharge air of the condenser may hit surfaces below dew point of the discharged air. In this case you need to treat these surfaces against moss and mildew.
If your condensers are too small so that you need to wet the finned surface then you will always face the same problems you are having and the only solution is to change to a larger condenser.
You can improve filtering the air before spraying to prevent dirt but this would bring other problems like fans that can cope with the increased pressure form the filter and larger working area, more maintenance for the filters, adequate filters, etc.
No easy "patch" solution for the dirt but the problem should reduce if you evaporate all the water first.
Low humidity in Malaysia, wrong. You live in the steamyist place on the planet during the what ever wet season. Last time in the area I broke into a sweat combing my little bit of hair.
was also a bit confused when our friend from malaysia said they have low humidity. i think our ambient condition here in the philippines, is identical with malaysia. we usually have an rh of 65 to almost 73 %
Shandong Shenzhou Refrigeration Equipment factory here, manufacturing Bitzer compressor
refrigeration equipment, Subcritical and Transcritical CO2 refrigeration system for cold storage, cold room, catering restaurant and supermarket with high quality and competitive price.
Hope to cooperate with you! Contact Email: refrigeration.shenzhou@gmail.com
But the right louvre moves nicely, it just does not open as far as a left one. It is always more closed, in all positions of the flow. I hope the technician will find time during the next week, but...
I prefer doing it the other way. I switch on my vacuum pump with only the vacmeter attached on it. I then can see if 1. my pump is pumping low enough and as low as the last time and 2. if my vacmeter...
the corresponding condensing temperature for 10 bar is 43 C which means the entering water temperature must be around 35 .. when you use a water with 39C the pressure increase, you can't change the...
also if you go on someone elses install, it cuts a lot of time, and your ever thankful to the dude who took the time to label every hidden joint- granted that he may be crap at brazing:p
no recalibration, just swap the louvre motor, probably worn gears inside causing slippage , they realign when powered off
MHI 20ZJX-S mislagned right and...