    Chiller HP Checks



    Hi everyone, first post.I've been told to go to one of our sites on Friday to show to the buildings insurance company that the HP/LP safety devices are working ok. Other than disconnecting the condenser fans(presuming its air cooled) how else would you go about doing it other than pumping down and testing with ofn.Also would you say is the best way to test LP just to carry out pump down on system? Thanks in advanced.Dave



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chiller HP Checks

    You could try lowering the HP setting pressure to prove the operation of the switch prior to testing at the design pressure.

    If you can detach the switch from the system then yes use OFN unless you have a controls tester pump.

    LP should b easier by performing a pumpdown.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Chiller HP Checks

    If chiller has transducers and a display screen use a multi-turn potentiometer ( 0 > 10kohm range )connect to plug on transducer and wind away and watch result on screen.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Chiller HP Checks

    Welcome to the forum readie2.

    I am confused as to why you are asking for LP checks.
    HP yes because it is a requirement for the pressure vessel regs.
    Never ever come across an Insurance Inspector that wanted to witness LP cutouts!

    As Brian states, with mechanical switches the easiest way is to lower the pressure towards the working pressure and witness when the comp cuts out.
    On software setting controlled versions again change the cutout, to just above the normal running and induce a higher pressure by switching of condenser fans.
    You need to know your Plant mind as there are some with internal bursting disks or no PRV'S.
    These may have to be approached differently.
    Grizzly

  5. #5
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Chiller HP Checks

    The best way for a novice is do a bench test like Brian_UK suggests! The problem is that you need a way to disconnect the devices without venting and vacuum the lines after reinstalling.

    You have to be careful to move the pressure slowly if you follow Magoo’s and Grizzly’s method or you could end up with wrong measurements ... if you don't have their experience!

  6. #6
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Chiller HP Checks

    Zurich Insurance for one usually ask to see LP trips / HP trips i doubt you will have enough time to test anything prior to showing the Insurance rep, plus with some HP's such as on Carrier 30GX in particular pretty hard to get to it or worse it can't be altered in situ due to how its fitted.
    The rep will also look at any PRV's fitted to see if they need changing (every 5 years)
    Last edited by Gibbo; 15-04-2012 at 08:41 AM.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Chiller HP Checks

    Quote Originally Posted by Gibbo View Post
    Zurich Insurance for one usually ask to see LP trips / HP trips i doubt you will have enough time to test anything prior to showing the Insurance rep, plus with some HP's such as on Carrier 30GX in particular pretty hard to get to it or worse it can't be altered in situ due to how its fitted.
    The rep will also look at any PRV's fitted to see if they need changing (every 5 years)
    Hi Gibbo.
    Funy thing is We annually test for Zurich on various site in the Southwest U.K.
    And have yet to be asked to trip a plant on *H.P.*
    (Sorry guys the H.P. should read L.P *)
    Would you happen to know why your Inspector is asking to test LP switches / settings?

    I would be very interested as to why.
    What sort of size plant are you talking about?
    Grizzly
    Last edited by Grizzly; 15-04-2012 at 02:38 PM. Reason: Being thick again!

  8. #8
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Chiller HP Checks

    Quote Originally Posted by Grizzly View Post
    Hi Gibbo.
    I would be very interested as to why.
    Grizzly
    The PSSR 2000 requires you to establish the safe operating limits (pressure and temperature) of the system.

    Readie2 may not have equipment information and is collecting this data from the switches?

  9. #9
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Chiller HP Checks

    Just did one last week and that was what he asked for but as the Carrier chillers did not have any LP's (30GX 082) he was ok and just concentrated on HP's and PRV's. Don't know why he wanted LP's I never asked, but i have been asked a few times to do it.

    Gibbo
    Last edited by Gibbo; 15-04-2012 at 09:59 PM.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chiller HP Checks

    They probably have the LP switch on their 'tick list' so it has to be looked at.

    Also, of course, because they are working from tick lists they may be concerned that the system will implode if the LP goes into a vacuum.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Chiller HP Checks

    Quote Originally Posted by Brian_UK View Post
    They probably have the LP switch on their 'tick list' so it has to be looked at.

    Also, of course, because they are working from tick lists they may be concerned that the system will implode if the LP goes into a vacuum.
    Thanks for the reply Gibbo.

    Brian.
    We are on the same wavelength.. No doubt about it!

    Readie2
    How did you get on?

    Grizzly

  12. #12
    readie2's Avatar
    readie2 Guest

    Re: Chiller HP Checks

    Thanks for all your replies. Turned up Friday and got familiar with the plant. Only to get a phone call from the insurance guy saying he was off sick and will be re arranged for this friday. I'll try again then!

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chiller HP Checks

    Tell him you want to see a Risk Assesment of his state of health before you allow him within coughing distance.
    Brian - Newton Abbot, Devon, UK