    Commissioning Sheets for Splits?



    I was recently contacted by a customer regarding some Daikin units that I had installed about 6 months ago.
    Where the customer was asking if he could have some commissioning sheets for the said equipment.
    I advised him that it was not normal practise to compile a commissioning sheet for splits, as they generally come pre charged.
    And that with the complex variable speeds etc etc.
    That most manufacturers simply require a test run with the unit ramped up and down using the Thermostat settings. Also as they have self diagnosis software etc. Further logging is not necessary.
    I explained that on the likes of close control equipment where physical adjustments are required. Then the manufacturers supply commissioning sheets.

    In short it is not normal to provide such for a split install.

    Or do others do differently?
    Grizzly



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    i agree , but 1 customer wants system operating pressures so it involved fitting gauges and logging pressures in both modes at full demand with the condenser running current as on mitsi/daikin splits it doesnt tell you inverter output-also you cannot record compressor load as the different voltage/frequency is innacurate- unless its a mitsi power inverter which will tell you comp current,fan output step,dc bus voltage,and target/actual frequency.
    so on every service visit,its not just a matter of bashing the filter and testing a pump,now its a bit more involved, and to aid this i got some 410a qwic couplers to prevent fridge gas loss and save me lil fingers from getting burnt- will send you a copy when i get some sheets tomorrow

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Commissioning Sheets for Splits?

    You do not need to take pressures to provide a commissioning sheet. We do a sheet with every install( don't we Kev).
    It logs make serial model refrigerant and quantity, pressure test, vacuum (often witnessed as these things can bite you on the bum) etc etc
    we don't take amps or pressures as on inverters that's irrelevant.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    The strength,leak and Vacuum tests are all logged and witnessed by the customer.
    The details of which I always put on my timesheet.
    But as for running parameters and attaching gauges I don't normally go there.

    We tend to adopt the "If it ain't broke don't fix it" attitude where splits are concerned.

    Grizzly

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    kev- rb is onto them generic comissioning sheets-ur gonna have to buy a clip on ammeter and gauges and a thermometer!

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    A completely irrelevant question springs to mind when reading this...

    When you guys say "But as for running parameters and attaching gauges I don't normally go there" how did you do the strength/pressure test and vacuum without gauges/a manifold attached?



    .

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    i think what grizzly is referring to is once pressure tested ,vacced and charged, comissioned- gauges are only then fitted if system poorly performs or an error code referring to pressure problems is indicated

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    OK. To Clarify.
    When completing the install having logged test pressure etc.
    By using a manifold and the relevant gauges.
    The system is then set to work (Or for the more pedantic.)

    The Suction and Discharge ports on the condensing unit are opened.

    From then on is it wrong to test run the A/C without the further use of gauges.

    Therefore my original question still stands.

    What amount of detail is normal when first running a newly installed a/c system?
    Irrelevant your question may be if I had explained further in the first place Viking.
    I rather assumed my question was simple enough!
    Grizzly

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    Quote Originally Posted by install monkey View Post
    i think what grizzly is referring to is once pressure tested ,vacced and charged, comissioned- gauges are only then fitted if system poorly performs or an error code referring to pressure problems is indicated
    Spot on IM.
    So does anyone have a sample Commissioning sheet?
    Or is it just as we discussed where initial logging is all that is done,
    Thanks Grizzly

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    ive not forgotten , im in the office tomorrow-they were getting a sample 1 sent for printing so i will have a look-the old ones were more chiller service sheets wanting oil pressure,oil diff delay etc

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    Bless you Sir.
    Steve.

  12. #12
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Commissioning Sheets for Splits?

    you can buy a pad of commisioning sheets in climet center

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    Quote Originally Posted by martinw58 View Post
    you can buy a pad of commisioning sheets in climet center
    Thanks for the heads up I will check it out.
    Grizzly

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Commissioning Sheets for Splits?

    Grizzly

    Will this one do you?
    Attached Files Attached Files

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Commissioning Sheets for Splits?

    ive emailed you the sheets
    Last edited by install monkey; 13-04-2012 at 06:02 PM.

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Commissioning Sheets for Splits?

    Thank You Guys.
    Frank, I have saved your form and IM I have received your email.

    Your Help is much appreciated.
    Grizzly

  17. #17
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Commissioning Sheets for Splits?

    Good sheet Frank! Try that in a spanish accent