Results 1 to 7 of 7
  1. #1
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Bitzer screw compressor type HSK 7451-80-40P



    Hi / Dears
    I have 2 Bitzer comp. one HSK & HSN the first -10 C : +40 C and other -35 C : 40 C . they have ECO connection . My question can i use the comp. type HSK in -35 C : 40 C too ?
    Thanks friends



  2. #2
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Bitzer screw compressor type HSK 7451-80-40P

    No!

    Depending on the type of refrigerant used, from -10 to -20°C the compressor motor will not cool enough with the refrigerant, motor protector will trip.

  3. #3
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Bitzer screw compressor type HSK 7451-80-40P

    Quote Originally Posted by aramis View Post
    No!

    Depending on the type of refrigerant used, from -10 to -20°C the compressor motor will not cool enough with the refrigerant, motor protector will trip.
    Thank you for your reply could you please tell me about the min. evaporating temp. and can i use it in NH3 refrigerant?

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Bitzer screw compressor type HSK 7451-80-40P

    definitly not ammonia as they are semi hermetics,

  5. #5
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Bitzer screw compressor type HSK 7451-80-40P

    You can get all the answers you want from the manufacturer's site www.bitzer.de.

    All manufacturers specify a minimum evaporating temperature for their compressors depending on the refrigerant and design (model).

    You cannot use Bitzer semihermetic screws with R717 only the open type (OSK), are suitable.

  6. #6
    mond13's Avatar
    mond13 Guest

    Re: Bitzer screw compressor type HSK 7451-80-40P

    as suggested above already the bitzer website offers an design tool with propper calculations. (also available as software to be downloaded)

  7. #7
    Join Date
    Dec 2006
    Location
    Iran
    Age
    43
    Posts
    55
    Rep Power
    18

    Re: Bitzer screw compressor type HSK 7451-80-40P

    I think also the coolpack software could help you on system analysis .

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •