Results 1 to 11 of 11
    Apr 2012
    Scotland
    5
    Updating R12 to 134a
    Hi guys, I'v been in the trade for almost 4 years now and still don't truly understand most things about changing a system from the likes of R12 to 134a.
    I have a job with an R12 unit that runs a glass doored drinks display, the compressor has seized and I have to price the job.
    I know I have to change the compressor (duh), the filter dryer and flush the old oil out of the system.
    What I'm wondering is if I will have to change the capillary tube or if the condenser and evaporator are going to be of the right size?
    If I do have to change these I doubt I will be able to to this job as I'v no idea how to calculate the length of capillary needed and only the vaguest idea of how to size the evaporator/condenser (I'v lost all notes from college )
    any advice you can give would be helpful.
    Jun 2010
    Yorkshire
    520
    14
    Re: Updating R12 to 134a
    Just stick with r 134a and poe and you should be ok. Usually when you retrofit 134a for r12 its only the Jil you need to worry about, it will only use slightly more electricity. It must be a very old unit if its got r12 in it, is it actually worth repairing?
    Training may be finished but experience is never complete.
    Feb 2012
    Bolivia
    270
    8
    Quote Originally Posted by chilliwilly View Post
    Just stick with r 134a and poe and you should be ok …
    This is correct only for HBP compressors and systems with evaporator temperature from -15C to +15. (After cleaning the system).
    The problem is that under -18C the heat transmission coefficients of R134a drop compared to R12 and you will need a larger compressor and change cap tube also.
    You will probably get by the same condenser and evaporator size though the operating differentials will change (should be larger) so to keep a 3star refrigerator you would probably operate in 4star conditions.
    Quote Originally Posted by Baw_Jaws View Post
    You should read about it then:
    http://www.emersonclimate.com/White%...WhtPaper_9.pdf
    And
    http://mea.emersonclimate.com/mea/pdfs/tech/9304.pdf
    First tear down failed compressor and find out the reason for its failure and correct it before installing the new one.
    Not just flush, clean because the POE oil will dissolve all the dirt the mineral oil deposited in the evaporator and suction.
    You may install a suction filter temporarily if you cannot clean the system.
    Maybe, you always have to check, but most probably not.
    Size evaporators and condensers is no big deal but you have to read manufacturer’s literature. The big problem here is you will probably not have information on your evaporator. But the compressor tables will help.
    You can get old cap tube tables from your compressor supplier, but they only go so far you always have to do this on a trial and error basis.
    Jun 2010
    Yorkshire
    520
    14
    Its only a drinks cooler so it should be ok, I have retrofit 134a and dropped in isceon 49 in place of r12 with only arguable neglegible differences.
    By the way what's a HBP pot anyway?
    Feb 2012
    Bolivia
    270
    8
    I agree.
    Depends: High Blood Pressure, Home Buyers Plan, Harry Bludger Potter or High Back Pressure
    Apr 2012
    Scotland
    5
    Thanks guys, you've both been a great help. Oh and thanks for the great links aramis, I'll be saving both pdfs to reread at leisure. You have any for ground freezing?
    Feb 2012
    Bolivia
    270
    8
    Wow! 4 years in the trade and you are already moving to mining engineering?
    http://www.bbri.be/homepage/download...ng.pdf&lang=en
    Apr 2012
    Scotland
    5
    np just interested is all.
    Apr 2012
    Scotland
    5
    oh and thanks again
    Apr 2012
    Scotland
    5
    hmmm little basic and doesn't show anything of how they counter the acceleration of water flow between the freezing pipes. I'll give google a shot again.
    Feb 2012
    Bolivia
    270
    8
    Water will not flow faster because it travels through the ground basically by capillary action.
    If the soil is too fluid, you must use more tubes and with nitrogen or co2 to freeze it fast.