    losing oil an d alot of back freezing



    hi guys i installed water chiller plant last year there aare two 40 hp compressor and one of them is losing oil and and alot of back freezin is happenig on the compresor
    -***** is 404A
    -there suction accumulator
    also there is oil separator



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: losing oil an d alot of back freezing

    Maybe liquid is entering the compressor and is foaming the oil...? Are the compressors connected to the same circuit / expansion device?
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: losing oil an d alot of back freezing

    Sandro Baptista mentioned one possibility but there are others and we need more data.

    Are these compressors in parallel and share refrigerant? If so, do they have oil level regulators installed?

    For one to freeze you must have lower pressure in that one, measure suction and crankcase pressure in both compressors and post it.

  4. #4
    Join Date
    Mar 2012
    Location
    USA
    Age
    53
    Posts
    4
    Rep Power
    0

    Re: losing oil an d alot of back freezing

    liquid flood back most likely cause. Is this a build-up chiller? Is it piped equal-distance? If these compressors are common to one circuit is the compressor loosing oil the lead compressor? Need more specific info to assist further.