    carrier book



    Hi guys im looking for info on a carrier unit the only nos i have are
    MUCV350C206
    TR160RYB
    0871S00104
    if anyone can help ??



  2. #2
    Join Date
    Apr 2012
    Location
    u.a.e
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: carrier book

    hi to all i have carrier 30gx screw chiller model 30gx267 ihave problem with this that compressor is running but there is not compression i mean pressure is not building and an alarm is comming 68 which is compressore oil alarm.i need help for this ..
    thanks in advanced

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: carrier book

    Low condenser air or water
    temperature, oil filters obstructed, oil
    valve blocked, oil solenoid and oil
    pressure transducer defective
    The 30GX/HXC screw chillers use one externally mounted
    pre-lubricating oil pump per circuit. This pump is operated as
    part ot the start-up sequence.
    ATTENTION: The operating temperature of the coil may
    reach 80°C. In certain temporary conditions (especially
    during start-up at low outside temperature or low condenser
    loop temperature) the oil pump can be reactivated.
    On 30GX units, the pumps are mounted to the base rails on the
    oil separator side of the unit. The pumps are mounted to a
    bracket on the condensers of 30HXC units. When a circuit is
    required to start, the controls will energize the oil pump first so
    that the compressor starts with correct lubrication. If the pump
    has built up sufficient oil pressure, the compressor will be
    allowed to start. Once the compressor has started, the oil pump
    will be turned off. If the pump was not able to build up enough
    oil pressure, the control will generate an alarm.

  4. #4
    Join Date
    Apr 2012
    Location
    u.a.e
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: carrier book

    thanks for the answer but the problem is compressor is running but there is not any action in dischare pressure or suction pressure . even i have change the internal oil filter if there is a problem with oil pump or oil selnoid valve the compressor will not be able to start. but the problem is compressore is start and after one minute it gets trip of alarm 68 and if there is nothing wrong with compressore then pressure should be builup.but there is not any action in pressure and standing is high side is 500 kpa .
    thanks in advanced for your answer and your replay

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45