Hi there,
I always use Danfoss TEV and they suggest that the TEV must be installed in a position that the liquid goes out from up to down. Also they suggest that TE2 models can be installed in a horizontal position but the vertical part to the distributor must be greater than 7xOD.
In an ALCO instruction I found that they suggest that the TEV can be installed in any position?
I far as I know the mixture of liquid and gas comes out of the TEV and the liquid must be distributed evenly through the evaporator circuits. Therefore, the liquid must be directed from up to down.
Any suggestion?