    Mcquay cenrtifugal chiller WSC - 079



    Hello friends

    I have a problem on operating McQuay centrifugal chiller Model WSC-079 (350 TR) , when swithing on the chiller the oil pump start running after short time , but the chiller dosent start , and the Microtech display shows ( vane open) , the oil pump pressure is O.K , if anybody know solution for this problem please help me.

    So many thanks

    My E-mail : kaled572003@yahoo.com



  2. #2
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Mcquay cenrtifugal chiller WSC - 079

    Hi Khaled,
    check vc switch, check unload solenoid and relevant output relay. VC switch requires a differential pressure of approx 3.5 bar to prove that the vanes are closed. the vanes need to be closed to prevent an overload current on start up.
    Also check that the service valve on top of the oil pot is not fully back seated as the 1/4" line is the drain line from the IGV.
    Last edited by ptsac; 17-03-2012 at 08:41 PM.

  3. #3
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    43
    Rep Power
    0

    Re: Mcquay cenrtifugal chiller WSC - 079

    so many thanks