water in the refrigerant circuit
Hi guys
my problem is that in the circuit of my chiller after a loss from the condenser is water in the circuit.
repaired after the leak and dehydrated all the components, I need to know what are the best techniques to remove all water from the circuit.
My experiences with small amounts of water have been resolved by the vacuum, but in this case the amount of water and a lot.
Thanks to all
-
17-03-2012, 08:27 PM #2
Re: water in the refrigerant circuit
lots of nitrogen,take the drier cores out and blast it slowly- triple vac use a torr gauge and try and warm the chiller,change the oil
-
17-03-2012, 08:50 PM #3
Re: water in the refrigerant circuit
fit a set of suction cores the biggest ones you can and do what im suggests
-
17-03-2012, 09:39 PM #4
Re: water in the refrigerant circuit
hi mark ,
as install monkey sayes ofn , but you can also heat the ofn < theres no liquid in ofn< and heat the chiller tubes with industrial fan assisted gas heater< this will help to boil off water < when vacing out
you could even run it on ofn < for a short time< to disipate the water,
ps remember to change the oil in the vac pump as well as the comp, sedgy,Last edited by sedgy; 17-03-2012 at 11:33 PM.
-
19-03-2012, 03:47 PM #5
Re: water in the refrigerant circuit
if you can get an air compressor with decent filtration to remove oil vapour running through a regen dessicant dryer, down to -60c You could leave in on over night or longer to blow out an water residue that`ll save a fortune on nitrogen. Then purge though with nitrogen and carry out the other works recommended by earlier posts.
-
17-06-2012, 05:21 AM #6
Re: water in the refrigerant circuit
lots of nitro,ice traps still gunna have to change oil constantly you need more than tripple evac when you start getting decent vac any moisture will freeze and you will think you got it all but as soon as pressure rise ice will liquify again heaters will will help stop water from freezing, good luck,ive seen these things go south before it can get messy .
-
17-06-2012, 07:43 AM #7
Re: water in the refrigerant circuit
Thanks for the responses everyone.