    In our facility we utilize Allen Bradley PLC software. In specific RS5000 & RS 500. I noticed in the refrigeration industry they make there own logic & HMI platforms. We are considering utilizing our PLC to write the Logic for our air handlers (Positive air) for the facility (Milk Plant). Does anyone here or has anyone used Allen Bradley as a platform for there controls.

    Thanks

    Joe



  2. #2
    Join Date
    Jan 2005
    Location
    Norfolk, U.K
    Age
    44
    Posts
    65
    Rep Power
    20

    Re: Control Question!

    There 's no reason why you cant use them.

    I have Mitsibishi FX2n PLC's With E200 HMI's controlling large refrigeration plants and they work very well, we had a few teething problems trying to get the program right but running smoothly now.

    Have a look at www.mrplc.com there may be some info there.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Control Question!

    There is no problem using a PLC to control the equipment. One thing I would caution you on is the control logic you write. The controls will do whatever you "tell" it to.

    Any control logic written for the equipment should be checked to make sure it does exactly what you want. The general requirements are:

    1) Basic control strategy
    2) Alarms
    3) Safeties

    One other aspect to be aware of is control speed. By this I mean, how fast does the system react to control changes? PLC's and electronic controls can operate in milliseconds. Refrigeration systems are more tolerant of low speed changes. Any sudden change in suction pressure can cause very interesting things to happen.

    My main point is this: any change you want to occur, should be done very slow to ensure the refrigeration system does not adversely react to the change.

    Slow, stable control is better than fast reactions to a change in input value.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Control Question!

    In my opinini, you can do it faster, cheaper, more reliable with standard controllers, specific made for this task.
    We use the Polygir for this. http://www.landisstaefa.co.uk/default.asp
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Nov 2005
    Location
    Moscow
    Posts
    20
    Rep Power
    0

    Re: Control Question!

    Hi balerjoe!
    Certainly you can apply AB controller if you would want that nobody, except you, understand yours AHU control system

    Otherwise better to use special configured controllers such manufacturers as Siemens, Honeywell,TAC,Trend, Carel, Regin and others...
    Last edited by Rfcont; 20-11-2005 at 08:35 AM.

Similar Threads

  1. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  2. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  3. Loading / Unloading Control Question...
    By Bluenoser337 in forum Industrial Compressors
    Replies: 31
    Last Post: 02-05-2006, 06:03 PM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •