    Hi guys,

    what is you're experience whit bivalent systems, for example the combination; gas-heating/heat pump or oil-heating/heat pump and so on.

    how do you combine them? in calculations i mean. is it 30% / 70% and most work is for the HP or the other way around?

    don't here much about the absorption heat pumps here, are they so perfect?

    love to here from you all,

    Ice



  2. #2
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: bivalent systems

    They work well on air to water systems where the oil/gas only kicks in when the outside temp drops below zero. They don't make any sense where they work in tandem on rads etc as the oil/gas ends up running constantly and the heatpump almost never.

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: bivalent systems

    The heat pump should be sized accordingly and the back up heating is
    only called on if the ambient temperature drops to a point where it
    can't cope unaided.

    There are many ways of controling this but the true bivalient system brings
    in the alternate heat source as the heatpump gets less effiecient and they run
    in parrallel (together) until the ambient drops to a point that the heat pump
    is inafectual.

    All the best

    coolrunnings

    .

  4. #4
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: bivalent systems

    Nearly all the HPs in the USA are dual source, especially the American made ones (not so much the Mitsis) and they have preset change over temps, typically from 0C to -5C depending on where you are in the country. There is no rule for the changeover temp but because they almost always heat through their ducted system, homeowners don't want the cooler air blowing. The only way to really fix it easily is to shut it off and turn on the gas.

    Glad i follow the European way heating water

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: bivalent systems

    Absorption system gets a 'COP' of nearly 0.7
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: bivalent systems

    I built my own system using a decomissioned Mitsubish unit and 100L water tank as a buffer. The idea was to pre-heat the water before it went to the boiler (oil) and then onwards through conventional (aluminium) radiators.

    It worked fantastically well over the winter. I reduced my oil consumption by nearly 90%. The boiler was only used for about 6 weeks. It's not a fully automated system (maybe I'll do that sometime) but my experience of combining the two heat sources has, from my point of view, proved that it can work extremely well.