Thread: city multi ymfc
-
14-03-2012, 06:56 PM #1
city multi ymfc
gents- city multi ymfc 410a 2007 outdoor address 58,bc 59 indoors 08-13 all present- sw1 1 2 10 on cannot detect 3 parf27 controllers-which are connected on 08,11,13- checked address on controllers-connected on the m net - 108,111,113- system still alarms on 000 6607
run it as a stand alone -disconnected the tb7 for the g50- still alarms- all indoor connections ok, outdoor-29vdc on mnet- swapped o...utdoor boards with another unit-changed address on rotary switches ok-still fooking alarms(have done virgin restart- also the g50 was connected to oudoors 51,58 couldnt detect system 58- refrigerant moniter only showed 51 outdoor 52 bc 1-7 indoors and controllers-couldnt detect system 58- tb7 link from 51-58 ok-mitsi suspect power pack on g50!- any ideas? ta
-
14-03-2012, 07:35 PM #2
Re: city multi ymfc
Fit a Daikin.....self addresses every time
-
14-03-2012, 10:01 PM #3
-
14-03-2012, 10:08 PM #4
Re: city multi ymfc
its been in for 4 yrs and was probably modified 2yr ago when the hotel was refurbished-we took over the repairs etc 8mth ago- dont know if its ever worked properly-as the system still operates with the fault code flashing-doesnt help with a site handyman-sticks his screwdriver in anything!- strange how the outdoor doesnt detect 3 controllers on the system- but the controllers work ok? also theres a few covers off the indoors so someones been poking about
-
17-03-2012, 09:03 AM #5
Re: city multi ymfc
i thought that sw1 1,2,10 only brought up the bc box addresses?
Last edited by Reffnut; 17-03-2012 at 09:12 AM.
-
17-03-2012, 03:59 PM #6
Re: city multi ymfc
Thats correct
In the words of David Byrne, Well...How did I get here?
-
17-03-2012, 08:00 PM #7
Re: city multi ymfc
sw 1 ,1 and 10 is indoor unit addresses 2,10 bc box address 1,2,10 remote controllers- i checked this on system 51 and all is displayed remotes,indoors and bc, but not on system 58
-
19-03-2012, 04:14 AM #8
Re: city multi ymfc
Hi IM, could you please check outdoor units' SW2-1s all should be ON so that your G-50A will decide the grouping of indoor unit and remote controller.
If SW2-1s are OFF, outdoor unit will decide the grouping.
I think one of the outdoor unit's SW2-1 is OFF position (may be system 58).
Hope this help for this issue.
-
19-03-2012, 08:06 PM #9
Re: city multi ymfc
sw2-1 is off( centralised controller) for all 8 outdoors- i checked system 51 and that picked up all indoor controllers,the g50 picked this up- with 51 and 58 connected only 51 exists on the g50, both outdoor pcbs were swapped to see if there was an issue,but still problems with 58
-
20-03-2012, 12:52 AM #10
Re: city multi ymfc
SW 2-1 ON for (all) both outdoor units. And register again in G-50A for groups.
RC must shown on the G50A, check all the registered groups one by one.
G01 should shown 001 indoor, 101 remote controller and so on.
Check all 13 indoor units you have.
G50-reg.jpg
-
20-03-2012, 01:30 PM #11
Re: city multi ymfc
As joe says the g50 wont picpk them up if it doesn't know it has to look for them.
Programme all units and initialise G50 again.
Cheers