    Mar 2012
    uk
    44
    1
    Help with chiller circuit pipework installation.
    I have been given the task of installing a chiller circuit to provide cooling to 3 machines. There are 2 chillers with inlets and outlets and they also want 2 plate heat exchengers installing in series.
    Can anyone shine some light on how to do this as im new to this.
    Thanks.
    Tom
    11,024
    Re: Help with chiller circuit pipework installation.
    Connect the 2 chillers via a circulating pump to a chilled water buffer vessel sized according to the chiller loads.
    Install flow swiches on both chillers. Install balancing valves or use a reverse return layout.
    Connecting the 2 PHE in series will provide two different heat loads as the second unit will have the higher temperature chilled water.
    Anyway, provide a second pumped circuit to the PHEs from the buffer vessel.
    I'm sure that others will come up with other/better ideas but that should give you the basics.
    Or, try a little reading first...thanks to Google..
    http://www.taylor-engineering.com/do...illedWater.pdf
    Auckland
    74
    3,357
    38
    Hi Tom
    a sketch is worth a thousand words, can you post any further details. Flow rates , temps, Kw duties forecasted.