    Best way to sense level of liquid refrigerant in receiver?



    What's the best way to electronically sense the level of refrigerant in a liquid line receiver? (Only 8 levels or so is enough.) Tiffany is asking me that for a future "mini mainframe" cooling system. The sensor can be either analog or digital. The refrigerant will be R410a if it makes a difference.
    Is the refrigerant electrically conductive? If so, would there be any undesirable chemical reactions by passing a small amount of electricity through it? If not, is there a substantial difference between the capacitance constant of liquid and gas phase refrigerant? And what's the best way to get the signal from inside the receiver? Could a 2 piece transformer be used to pass power to the sensor and the signal to the micro? Are there better ways of sensing the level?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Best way to sense level of liquid refrigerant in receiver?

    Try this:

    http://www.hantech.com/documents/PDF/p109.pdf

    This should help to explain some of your questions.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Best way to sense level of liquid refrigerant in receiver?

    Bitzer has a standard piece of electronic to measure level in a vertical vessel.

    You can measure it ultrasonic or use the capacitance to measure the level (like they do in the fuel tanks of an airplane, two hollow cilinders in each other an a Wheatstone bridge as far as I can remember)

    Daikin and Mitsubishi are heating a small wire in the vessel and and a wire submerged in liqud will give another reading then one in the gasfase of the refrigerant.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM
  2. Liquid refrigerant and bubles in sightglass
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 30-08-2003, 09:07 PM
  3. Liquid Refrigerant Pumping
    By bersaga in forum Technical Discussions
    Replies: 34
    Last Post: 09-08-2003, 08:07 PM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •