    Mar 2012
    turkey
    43
    9
    Question DAIKIN FXFQ80P9 information about water condensation
    hi everybody ;
    I need information about water condensation for daikin FXFQ80P9 indoor unit. There ll be about 1500m3/h air at 35C and with %80 humadity and it ll be cooled for 10C and %50 humadity . My question is how many kg water ll be condensated in 1 hour? Sorry for my English but I ll be glad if someone explain and find me a solution.
    Mar 2012
    turkey
    43
    9
    Re: DAIKIN FXFQ80P9 information about water condensation
    any idea ?
    5,667
    To calculate kg/hr moisture removal
    kg/hr = vol x delta kg/kg x 3600 / specific volume
    You need to use a Psychrometric Chart
    from your figures - 35C @ 80% and 10C @ 50% the results are
    Vol = 0.416m3/s
    Delta kg/kg = 0.0256
    Sp Vol = (0.806 + 0.914/2) = 0.86
    so
    kg/hr = 0.416 x 0.0256 x 3600 / 0.86 = 44.57
    Looking at the spec sheet for the FXFQ80P9 it will not handle the volume or the humidity
    The maximum volume on high speed is 1410m3/hr but more importantly, it is only rated at 9.9kW cooling duty and you need 15kW
    Split Croatia
    6,151
    What you asking is this:
    That is if you have dehumidifier which will dehumidify all new air in one pasage. But, that is not your case.
    You have air-conditioner which will cool same air and dehumidify it in multiple pases through it.
    This is from tehnical data:
    At begining you will have this:
    At end you wil have something like this:
    Mar 2012
    turkey
    43
    9
    thanks for help. i ll look for thoose softwares if they can help me