DAIKIN FXFQ80P9 information about water condensation
hi everybody ;
I need information about water condensation for daikin FXFQ80P9 indoor unit. There ll be about 1500m3/h air at 35C and with %80 humadity and it ll be cooled for 10C and %50 humadity . My question is how many kg water ll be condensated in 1 hour? Sorry for my English but I ll be glad if someone explain and find me a solution.
Thanks
-
12-03-2012, 12:24 PM #2
Re: DAIKIN FXFQ80P9 information about water condensation
any idea ?
-
12-03-2012, 03:23 PM #3
Re: DAIKIN FXFQ80P9 information about water condensation
To calculate kg/hr moisture removal
kg/hr = vol x delta kg/kg x 3600 / specific volume
You need to use a Psychrometric Chart
from your figures - 35C @ 80% and 10C @ 50% the results are
Vol = 0.416m3/s
Delta kg/kg = 0.0256
Sp Vol = (0.806 + 0.914/2) = 0.86
so
kg/hr = 0.416 x 0.0256 x 3600 / 0.86 = 44.57
Looking at the spec sheet for the FXFQ80P9 it will not handle the volume or the humidity
The maximum volume on high speed is 1410m3/hr but more importantly, it is only rated at 9.9kW cooling duty and you need 15kW
-
13-03-2012, 03:13 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: DAIKIN FXFQ80P9 information about water condensation
What you asking is this:
That is if you have dehumidifier which will dehumidify all new air in one pasage. But, that is not your case.
You have air-conditioner which will cool same air and dehumidify it in multiple pases through it.
This is from tehnical data:
At begining you will have this:
At end you wil have something like this:
Last edited by nike123; 13-03-2012 at 05:04 AM.
-
13-03-2012, 03:36 PM #5
Re: DAIKIN FXFQ80P9 information about water condensation
thanks for help. i ll look for thoose softwares if they can help me