Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2012
    Location
    turkey
    Age
    43
    Posts
    9
    Rep Power
    0

    Question DAIKIN FXFQ80P9 information about water condensation



    hi everybody ;

    I need information about water condensation for daikin FXFQ80P9 indoor unit. There ll be about 1500m3/h air at 35C and with %80 humadity and it ll be cooled for 10C and %50 humadity . My question is how many kg water ll be condensated in 1 hour? Sorry for my English but I ll be glad if someone explain and find me a solution.

    Thanks



  2. #2
    Join Date
    Mar 2012
    Location
    turkey
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: DAIKIN FXFQ80P9 information about water condensation

    any idea ?

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: DAIKIN FXFQ80P9 information about water condensation

    To calculate kg/hr moisture removal

    kg/hr = vol x delta kg/kg x 3600 / specific volume

    You need to use a Psychrometric Chart

    from your figures - 35C @ 80% and 10C @ 50% the results are

    Vol = 0.416m3/s
    Delta kg/kg = 0.0256
    Sp Vol = (0.806 + 0.914/2) = 0.86

    so

    kg/hr = 0.416 x 0.0256 x 3600 / 0.86 = 44.57

    Looking at the spec sheet for the FXFQ80P9 it will not handle the volume or the humidity
    The maximum volume on high speed is 1410m3/hr but more importantly, it is only rated at 9.9kW cooling duty and you need 15kW

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: DAIKIN FXFQ80P9 information about water condensation

    What you asking is this:



    That is if you have dehumidifier which will dehumidify all new air in one pasage. But, that is not your case.
    You have air-conditioner which will cool same air and dehumidify it in multiple pases through it.

    This is from tehnical data:




    At begining you will have this:



    At end you wil have something like this:

    Last edited by nike123; 13-03-2012 at 05:04 AM.

  5. #5
    Join Date
    Mar 2012
    Location
    turkey
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: DAIKIN FXFQ80P9 information about water condensation

    thanks for help. i ll look for thoose softwares if they can help me

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •