Thread: Rotary isolater
06-03-2012, 12:50 PM #1
Rotary isolater
Hi all quick question and bare with me I'm new to this. When ordering a rotary isolater I was asked what pole I wanted I know it's a 3 phs 32 amp but what pole ?? How do you know what pole you require
06-03-2012, 12:56 PM #2
Re: Rotary isolater
The pole is the switch so a
single pole is one switch, that would be the live
double pole is two switches, that would be live and neutral
three pole is basic 3 switches, that would be basic three phase
four pole is 4 switches , that would be three phase and neutral.
All switched with the same knob, lever, hadle or what ever its called.
Hope that helps
taz
06-03-2012, 02:09 PM #3
Re: Rotary isolater
and you need 4 pole isolator.
06-03-2012, 02:31 PM #4
Re: Rotary isolater
Thanks guys that clears that up
06-03-2012, 09:32 PM #5
Re: Rotary isolater
inverters recommend not using a pole for switching the neutral- it should be on a terminal block