    Remote condenser



    Hi all!

    If you need to remove heat loading, for example 500 KW, what way you prefer:
    1. install one remote condenser 500 KW
    2. install two remote condensers on 250 KW each in parallel
    3. install 5 remote condensers on 100 KW each in parallel
    What decision is better and why?

    Thanks!



  2. #2
    Join Date
    Nov 2005
    Location
    Denmark
    Age
    50
    Posts
    8
    Rep Power
    0

    Re: Remote condenser

    That depends!

    Is it a constant heatload?

    If it's constant you might as well use one condenser with fan control. Preferrable with speedcontrol on the fans instead of on/off control. And in Moscow you might need some condensing pressure reg. during the wintertime.

    If it's a variable load you should consider more condensers with some kind of condensing pressure reg. valve. combined with fan control and some solenoid valves so you can cut off some condensing capacity.

    R. Nielsen

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Remote condenser

    You should check the size of the area, is it big enough?
    The cost of the project.

    all of your ideas will do the job.

    Chemi

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Remote condenser

    I would modify option 2 and install 3 x 250kW. You now have some capacity control, albeit coarse, and some spare capacity for overload, breakdown or maintenance.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Nov 2005
    Location
    Moscow
    Posts
    20
    Rep Power
    0

    Re: Remote condenser

    to me I'd prefer the first way and that is why:
    I think, that dividing of heat loading into some parts will lead to serious lowering presure drop in condenser system and at work during hot time of summer, whole condenser system can be a disbalancing.
    Also regulation of head pressure by cycling of the fans can be more complicated

    Regards,

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Remote condenser

    One 500 kW condenser with fan cycling control to regulate pressure.
    When you cut off a condenser with a SV, you first have to pump it down so that no liquid remains in the condenser. And you will need 2 SV's (in and out), otherwise the not working part of the condenser can fill up backwards with liquid. In my opinion, not such a good idea.
    If very low part load associated with low ambient is a possibility, install a condensing pressure regulator, a differential pressure flow valve (NRD of Danfoss) so that liquid is stored in the condenser to decrease condenser surface area and make sure that your receiver is big enough.
    Or even better, use a EEV so that you can use all the benefits of a low HP and let it run on a low HP.

    Connecting parallel different condensers, even from different size (different DP across the condenser) is not that difficult, as long as you use the proper rules to do this.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Nov 2005
    Location
    Alberta, Canada
    Age
    46
    Posts
    13
    Rep Power
    0

    Re: Remote condenser

    Whats the load? Constant? variable like a rack?
    If constant I would recomend single cond due to price and ease of setup/install.

    Variable load would come down to how much of a load variable are we talking about. Multiple condensers are great in low amb conditions like up here in Canada where -30c is common. Its quite allot more money to put in a multiple condenser system but you are able to keep a good handle on the design liquid pressure. Var speed fan on the condensers are expensive and not really needed unless the amb temps will fall down to the -30 range for long periods of time.
    Ever think about split coils? One condenser with multiple headders. Best of both worlds

    To give you and example of a typical multi condenser setup for a variable load would be the systems used in some supermarkets around my area. 200+ HP rack with 2 condensers. First condenser is split in half and the second condenser is the same size but non split.
    So what we have is 100%,50% and 25% split ability. We also use a variable speed fan on the lead fan on the full time 25% condenser that allows us to run low condensing temps year round without having liquid logging problems.

    clear as mud?
    their is NO hard fast rule, never is, the best way to approach is to look at each individual application and ballance price and function.

  8. #8
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Remote condenser

    it depends on ambient temp - if you choose as amb.temp. +28 - you can find this condenser.

    if +34 - you simply can not find such condenser!

    plus - size of condenser, sound.

    and you must have KVR+NRD for winter. In our country it is usual run of things - temp minus 20 Grad C in winter.

Similar Threads

  1. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  2. Check your remote.
    By Temprite in forum Air Conditioning
    Replies: 11
    Last Post: 26-05-2006, 08:21 AM
  3. Remote condenser + heat recovery
    By Renato RR in forum Technical Speculations
    Replies: 9
    Last Post: 30-03-2006, 07:26 AM
  4. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM
  5. Remote Control problem
    By botrous in forum Air Conditioning
    Replies: 2
    Last Post: 12-10-2005, 05:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •