    Sizing walk-in cooler, freezer cheat sheet
    Hi there, I had a chart for a few good years, lost it. Well, i found it today and want to share it with you guys.
    Page 43.
    http://www.heatcraftrpd.com/products/PDF/Misc/EM.pdf
  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19
    Re: Sizing walk-in cooler, freezer cheat sheet
    thanks for information.
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46
    Interesting read Thanks.
    Grizzly
  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37
    A quick check I do with installed systems that may be overloaded is do a quick estimate of external box area, floors walls and ceiling for what ever application. then multiply external area expressed in square feet and multiply by 16 for chillers and 13 fo freezers, result is in Btus for standard applications, works everytime. You get a feel for actual application and refrig system sizing as installed, only for small stuff though.