Results 1 to 5 of 5
-
02-03-2012, 02:58 AM #1
Sizing walk-in cooler, freezer cheat sheet
Hi there, I had a chart for a few good years, lost it. Well, i found it today and want to share it with you guys.
Page 43.
http://www.heatcraftrpd.com/products/PDF/Misc/EM.pdf
-
02-03-2012, 04:20 AM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Sizing walk-in cooler, freezer cheat sheet
thanks for information.
-
02-03-2012, 08:16 AM #3
Re: Sizing walk-in cooler, freezer cheat sheet
Interesting read Thanks.
Grizzly
-
03-03-2012, 04:52 AM #4
Re: Sizing walk-in cooler, freezer cheat sheet
A quick check I do with installed systems that may be overloaded is do a quick estimate of external box area, floors walls and ceiling for what ever application. then multiply external area expressed in square feet and multiply by 16 for chillers and 13 fo freezers, result is in Btus for standard applications, works everytime. You get a feel for actual application and refrig system sizing as installed, only for small stuff though.
Ten minutes with a tape measure and a calculator.
-
03-03-2012, 06:20 PM #5
Re: Sizing walk-in cooler, freezer cheat sheet
interesting, the numbers tend to match right on.