    Carrier 2 1/2 Ton Air to Air HP performance.



    Hi every one,
    I just took some temperature and air flow readings at my indoor "A" coil. The vapour line temp
    seems high.
    Do these numbers look OK or do I have a problem?

    pilko
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Carrier 2 1/2 Ton Air to Air HP performance.

    It may be but what is the refrigerant as the temperature on it's own does not relate to anything?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2011
    Location
    Canada
    Age
    78
    Posts
    79
    Rep Power
    13

    Re: Carrier 2 1/2 Ton Air to Air HP performance.

    Thanks for the response Brian.

    The refrigerant is R22.

    pilko

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Carrier 2 1/2 Ton Air to Air HP performance.

    Discharge does seem a little low, but this just could be down to losses, from comp and piping.
    Is frost on out door unit fairly/ice even when running
    But looks OK