    Hi Guys. After some help with a Toshiba A/C System. Model No RAV-SM803 AT-E.
    Runs fine in cooling mode. When switched to heating mode pressure rises to 248psi and compressor cuts out. Condenser fan continues to run compressor restarts runs to 248psi and cuts out again.
    3,856
    Re: Toshiba A/C
    What are the filters like?
    Feb 2008
    504
    21
    Re: Toshiba A/C
    check air filter and coil
    Feb 2008
    504
    21
    Re: Toshiba A/C
    is the indoor fan running if nit check coil sensor
    Oct 2007
    manchester
    5,639
    45
    lakeland's Avatar
    lakeland Guest
    Re: Toshiba A/C
    Thanks for the replys. The filters are clean as is the coil. The evap fan doesnt cut in because coil temp is to cold.
    Feb 2008
    504
    21
    Re: Toshiba A/C
    sounds like a faulty hp switch i have service manual if you send me your email
    AMAC's Avatar
    AMAC Guest
    Re: Toshiba A/C
    Check your sensors... They should all be 10KOhms at 25C except for the compressor sensor which should be 50KOhms at 25C. Has it gone on fault...