    how to increase the capacity of an refrigeration system



    hi,
    iam doing a project on refrigeration system. the problem is that the original capacity is 90 tonne. but now we are getting only up to 45 to 50 tonne. the refrigerant used is *****. it is used for cooling chlorine to -5degree. the system consist of a screw compressor (vertical,single stage) , oil seperator, condensor , reciever , expansion valve and an liqufier. an ecnomizer is there but now it is not used.
    so please help me in this matter to increas the capacity of the unit to much higher value



  2. #2
    Join Date
    Feb 2012
    Location
    Canada
    Age
    38
    Posts
    1
    Rep Power
    0

    Re: how to increase the capacity of an refrigeration system

    "the refrigerant used is *****"?

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: how to increase the capacity of an refrigeration system

    are you directly cooling or are you using a heat exchanger have you tried reconecting the economizer

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: how to increase the capacity of an refrigeration system

    Get the economizer operating for a start, that will increase capacity approx 15%, Pump system down and drain oil from evaps, recommission system to suppliers original specs.