    Trane ECGCL chiller running - limit



    I have a Trane ECGCL600 chiller that will only run on limit, the condensor fans run slow speed but the compressors won't kick in, display is as follows

    Chiller Mode - Running - Limit
    CCT1 - Running
    CCT2 - Running
    Evap ent/ lvg Temp - 22.6/22.7
    Active CW Temp - 10
    Active demand Limit Temp SP - 100%

    Reports
    CCT1 Evap sat rfgt temp - 15
    suct press - 655.7 kpag
    evap approach temp 7.6

    Any suggestions most welcome. ( a guy from Trane recons its running on limit because flow is above 15 degrees ?? but aint thats what the chiller is for)



  2. #2
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: Trane ECGCL chiller running - limit

    It seems water T is to high. Reduce heat load temporary an let temperatute drop below 15C.

  3. #3
    Join Date
    Oct 2011
    Location
    Esztergom
    Age
    48
    Posts
    3
    Rep Power
    0

    Re: Trane ECGCL chiller running - limit

    The high water temperature may be due.Check the:Configuration menu-CW High limit/Factory setting +15˘C/. The set limit value is reached at the equipment.I hope I helped some.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Trane ECGCL chiller running - limit

    Hi kkeith2.
    May I ask what is the pd across the evap?
    Secondly what's the Subcooling temp?

  5. #5
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane ECGCL chiller running - limit

    Ok, this is an old-ish thread, but for the benefit of anyone else with a similar question:

    The guy from Trane is right. With a water temp. over 15°C, the chiller will run on limit mode to pretect itself from nuisance trips / possible damage due to the excessive heat load. [Chilled water systems are designed (usually) for around 12°/7°C in/out]. Once the chiller gets the water temp below 15°C, it will start to load up.
    It's standard on all Trane chillers.

  6. #6
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane ECGCL chiller running - limit

    check the calibration of all components, as well as water velocity, the display tells you that are running limit scroll compressors, if possible tell me what type of refrigerant is the machine