Results 1 to 4 of 4
  1. #1
    Join Date
    Nov 2010
    Location
    Poland
    Posts
    40
    Rep Power
    0

    Bitzer tandem compressors and check valves



    Hello again my dear Friends.

    This time i have a small question about compressor like one in that link: http://pdf.directindustry.com/pdf/bitzer/semi-hermetic-recip-compressors-tandem-kp-110-3/17562-114281.html

    a
    nd check valves... in my opinion it is like two separete compressors connected in parallel so i have to put in check valves on both discharges.

    Am i right?

    Thanks for opinions, Marcin
    Have a nice day!



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Bitzer tandem compressors and check valves

    Certainly a good idea to add individual discharge check vavs, plus oil balance line as well.

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Bitzer tandem compressors and check valves

    Check valve on each compressor , gas balancing line and of course oil balancing line as mentioned in magoo`s post. If low evaporating temp below minus 15 deg c an oil separator would be requd

  4. #4
    Join Date
    Nov 2010
    Location
    Poland
    Posts
    40
    Rep Power
    0

    Re: Bitzer tandem compressors and check valves

    Hi,

    Thanks for replays. That is what i exactly thought .

    Bye!