    dixell controller
    Hi, came across a freezer with a Dixell XR60CX controller. Condensor is icing up as the defrost is not working. Uses electrical defrost heater, and when defrost is on there is no power coming out defrost wire from controller. Thing is electrical drawing for controller shows 8 connections. 1=power in, 2=fan motor, 3=compressor, 4=power in, 5=neutral, 6=power to switch defrost, 7=defrost output and 8=NC.
    There is nothing connected to 6, so wondering if I can bridge power from 4 to 6 without damaging controller. Other engineer fitted new controller so I dont know what happened with connection to 6. Either this needs power or power goes through controller and it is faulty.
    Any ideas,
    Jul 2010
    Ireland
    52
    Re: dixell controller
    Hi there,yes there should be power on no6 usually taken off the same supply as no1 your control circuit.
    Oct 2007
    manchester
    44
    5,707
    https://rapidshare.com/files/3025425073/XR60CX_GB.PDF;
    according to the wiring diagram 1 is live in 2 output to defrost element, 4 is evap fan 5 is compressor signal 6,7 is ur 240v supply- when manually defrosting ensure the controller displays the defrost symbol and listen to the click of the relay- if no click- whack it with a screwdriver handle as the relay is probably sticking-change the controller-job done
    Jul 2010
    scotland
    43
    68
    8
    Quote Originally Posted by install monkey View Post
    according to the wing diagram 1 is live in 2 output to defrost element, 4 is evap fan 5 is compressor signal 6,7 is ur 240v supply- when manually defrosting ensure the controller displays the defrost symbol and listen to the click of the relay- if no click- whack it with a screwdriver handle as the relay is probably sticking-change the controller-job done
    There are three ways to wire this controller, and the way I described it is how the one I am looking at is done, with the exception of the no 6 block.
    Oct 2007
    manchester
    44
    5,707
    that wiring diagram is for the xr60c with the 20amp rated contacts-u said xr60cx,16amp contacts and either 240 or 12v control power, which is wired differently- but yes fit the link wire so live goes 1-4-6
    Jul 2010
    scotland
    43
    68
    8
    Ok, bridged the 4 and 6 terminals and the freezer now defrosts.