    r22/r404a tev



    over here you cannot get well not easily r22 valves,now the guys i use to supply me say for an r22 valve use a 404a valve so if so will a r22 valve work on 404a i just need to hear comments?its expansion valves i am referring to thanks.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: r22/r404a tev

    It think the guys at wholesaler are good salesman, if they gaurantee operation well OK. I think the TX will operate irratically, due to power element charge. There was a post on the forum about recharging power elements with different refrigerants, cannot recall the outcome.

  3. #3
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: r22/r404a tev

    ive used a 407c valve on 22 systems or i have used one of those multi use tevs out of rsl for 22 units

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: r22/r404a tev

    All TXV's from the same manufacturer and same series have exactly the same body, orifice has nothing to do with type of refrigerant. The difference is the charge which open the open and closes the needle when it senses the evaporator outlet.
    I have stopped looking at the refrigerant type on the TXV, only the temperature range.
    just yesterday I have installed R-134 TXV on a R-422D system, runs perfect.
    To my opinion and experience, it doesn't matter and I will use whatever is on the shelf.

    I suggest you give it try and see for yourself, saves a lot of headache.