    Sabroe smc100 lp hp



    Could anyone please advise actual difference with Sabroe suction & discharge valve on
    LP & HP valves.

    Is it simply the number of valve springs, or is there more to it?

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Sabroe smc100 lp hp

    Hi Ranger.
    I have to admit I am not totally sure as to what you are asking?
    I think you may be asking about when installed in either the LP or HP side of a compound machine,
    is that it?

    If so then the attached may help?
    Grizzly

    Attachment 8636

  3. #3
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    Hi Ranger,
    the difference is the number of springs on discharge valve. this was introduced with the MK3 serie. you need 6 spring/cyl on LP side and 8 on HP side. then you can get some problems with MK1 and 2 discharge valves because some holes are missing...the retaining plate is also differentNEW PARTS SMC 100.pdfressort-SMC 100 MK3.pdf

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Sabroe smc100 lp hp

    Quote Originally Posted by cricri View Post
    Hi Ranger,
    the difference is the number of springs on discharge valve. this was introduced with the MK3 serie. you need 6 spring/cyl on LP side and 8 on HP side. then you can get some problems with MK1 and 2 discharge valves because some holes are missing...the retaining plate is also differentNEW PARTS SMC 100.pdfressort-SMC 100 MK3.pdf
    Thanks cricri.
    I am also wondering now as there are different part No's for the valve plates?
    Grizzly

  5. #5
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: Sabroe smc100 lp hp

    Can i prevent evenly lifting plate?

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    hi Ranger
    also there is different between valve plate on NH3 and HCFC.

  7. #7
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    the ring plate are the same , but the retaining plate are different according if it's ammonia or hfc. I don't understand your question Josef.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    We are looking at converting a NH3 booster machine to high side, so Sabroe recommend
    changing discharge valve assy as well as internal relief valve.
    It looks like discharge valves have one more spring 7 compared to 8.

    Sound hardly worth worrying about to me, but who am I to say.
    Internal relief is 14 bar, so marginal sizing for high side duty.

  9. #9
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Sabroe smc100 lp hp

    If the internal relief is 14 bar, it's probably only affected by the difference between discharge & sump pressure. Assuming high side suction of 200kpa, 1400kpa internal relief takes you up to 1600kpa delivery - probably ok for most applications.

  10. #10
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    I do not saying you do as same as I did ,
    about 4 years ago we repaired one smc 16-100 s and we were in harry and we were short off discharge valve in our stock so I used HCFC valve plate to run system and later we go to change it. I checked it 3 times and it is same as NH3 and still is working. our system is running -15 + 35.

  11. #11
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    Ranger, your SMC100 is MK 1,2,3 or 4?

  12. #12
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    Quote Originally Posted by cricri View Post
    Ranger, your SMC100 is MK 1,2,3 or 4?

    cricri MK3 compressor

  13. #13
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    Quote Originally Posted by HVACRsaurus View Post
    If the internal relief is 14 bar, it's probably only affected by the difference between discharge & sump pressure. Assuming high side suction of 200kpa, 1400kpa internal relief takes you up to 1600kpa delivery - probably ok for most applications.

    Totally agree, but new ones are balanced port I believe.
    Knowing that, I think we have to update it in the interest of everyone.

  14. #14
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    Quote Originally Posted by mbc View Post
    I do not saying you do as same as I did ,
    about 4 years ago we repaired one smc 16-100 s and we were in harry and we were short off discharge valve in our stock so I used HCFC valve plate to run system and later we go to change it. I checked it 3 times and it is same as NH3 and still is working. our system is running -15 + 35.

    Would the HCFC plates have more valve lift, more springs, or both?

    With Mycom you could use ***** machine on ammonia, but not the other way.
    Now they just make ***** type machine, as its easier to keep stock of on machine than two.

  15. #15
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Sabroe smc100 lp hp

    comments removed as being an idiot!

    SOS
    Grizzly
    Last edited by Grizzly; 20-02-2012 at 09:06 PM.

  16. #16
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Sabroe smc100 lp hp

    Hi, RANGER1,

    Quote Originally Posted by RANGER1 View Post
    We are looking at converting a NH3 booster machine to high side, so Sabroe recommend
    changing discharge valve assy as well as internal relief valve.
    It looks like discharge valves have one more spring 7 compared to 8.

    Sound hardly worth worrying about to me, but who am I to say.
    Internal relief is 14 bar, so marginal sizing for high side duty.
    Do you have a TSMC-two stage (108/116) type and like to convert it complete to high stage or you have a normal SMC-single stage (104/108/112/116) working on low stage and now you need it to work on high stage?

    What about literature you have?


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  17. #17
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    Josip, Its a SMC108L running as a booster at the moment.

  18. #18
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Sabroe smc100 lp hp

    Hi Ranger, I explained in a private message to one of us:
    what I can say is:
    - it's always the same spring
    - the number of springs depend of the discharge pressure and the refrigerant, see my attached file on RE "ressorts...
    - the retaining plate change with the refrigerant and the number of holes needed for the springs
    ammonia, 1 grove on the suction and discharge retaining plates
    HCFC HFC, 2 groves .......
    this difference allow to the ring plate more "stroke" and more way for the refrigerant HFC HCFC
    (then it's possible to use HFC retaining plate with ammonia but not the reverse.)
    the discharge retaining plate is also marked (Mk3&4) LP;HP;VHP on the upside
    this difference is particular to Sabroe, most of the other brand make no difference between ***** and ammonia
    about the safety valve Mk3 compressors are fitted with safety valves independant from the suction pressure. the 14 is designed for the low stage of a TSMC code 3137-046 you need 3137-007 22bars

  19. #19
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sabroe smc100 lp hp

    Thanks everyone for your input

  20. #20
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Sabroe smc100 lp hp

    Hi, RANGER1

    Quote Originally Posted by RANGER1 View Post
    Josip, Its a SMC108L running as a booster at the moment.
    Then is enough to install appropriate number of springs on valves and change by-pass valve.

    Standard for one and two stage (HP) compressors is with preset opening pressure of 24 bar (348psi).

    Special for one and two stage (HP) compressors is with preset opening pressure of 22 bar (319 psi) delivered only in special cases according to local rules and regulations.

    Standard for two stage (LP) compressors 12 bar (174psi).

    Opening pressure is independent of the pressure on the suction side of the compressor.



    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.