    Replacing condenser after comp failure



    Hi all just a quick question I've been told to replace a condenser with a seized comp with a full new condenser. My question is if the previous unit had a seized comp and I'm putting a new condenser on the same pipes then do I need to install a drier to filter out any impurities when I install new condenser



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Replacing condenser after comp failure

    I would say yes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    Cheers Brian

    I thought so but nobody has mentioned it in the job brief or given me time to return and remove the filter drier at a later date once it's done it's job. I better mention it

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Replacing condenser after comp failure

    You don't need to replace the condenser. Its the compressor you have a problem with.
    A drier is to be changed every time you open the system.

  5. #5
    Join Date
    Dec 2010
    Location
    pakistan
    Posts
    4
    Rep Power
    0

    Re: Replacing condenser after comp failure

    you dont need to replase filter

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Replacing condenser after comp failure

    Yes you do !! As Chemi and Brian have both pointed out.
    Cheers
    Stu
    Quote Originally Posted by pepsiqazi View Post
    you dont need to replase filter
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  7. #7
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    It a long and drawn out story but in this server room we have 2 x systems I noticed on a maintenance visit sometime ago the first unit had a leak on the condenser coil. Because they still had one unit operating they didn't give me go ahead to carry out repair. Anyway a week ago second system went down with seized comp priced to replace but lead time on spares 3 weeks. So they gave go ahead to repair system with leak found that coil had had it so priced to replace coil. Again 3 week delivery. 3 day delivery for new outdoor so they have gone for that option. So changing condenser with bad comp for new condenser. But no mention of installing drier. Just been told to recover gas split flares and replace for new
    Last edited by Kirky; 18-02-2012 at 02:29 PM.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Replacing condenser after comp failure

    Are we dealing with an split ac unit?

  9. #9
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    Yes mate a split system. A LG P08AH if memory serves double fan double comp
    Last edited by Kirky; 18-02-2012 at 06:33 PM.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Replacing condenser after comp failure

    In that case, you might as well replace the outdoor unit, less work and time.

  11. #11
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    Yes mate that's the plan putting new outdoor in but using same indoor and pipes just haven't been asked to put a suction filter drier in case there is any **** in the pipes from previous comp failure or will it be ok with us changing out the whole outdoor. As a rule would always filter system after comp failure but don't usually swap out whole outdoor without swapping indoor and pipes

  12. #12
    Join Date
    Jan 2012
    Location
    usa
    Age
    58
    Posts
    1
    Rep Power
    0

    Re: Replacing condenser after comp failure

    i am new to this site and have enjoyed reading the discussions. that being said, i was surprised to see how this question could have these different answers. you always, always change the filter drier every single time you open a system.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Replacing condenser after comp failure

    Quote Originally Posted by Kirky View Post
    Yes mate that's the plan putting new outdoor in but using same indoor and pipes just haven't been asked to put a suction filter drier in case there is any **** in the pipes from previous comp failure or will it be ok with us changing out the whole outdoor. As a rule would always filter system after comp failure but don't usually swap out whole outdoor without swapping indoor and pipes
    Have done similar with a dead mitsi unit, would advise blowing through the pipes with some ofn, one we did chuffed all its oil out into the evap and pipe run and kept going out on a vacuum till blown through... Think i'd do an acid test to see if it needs a drier, job to tell as if it did have one it should be taken out again after a while but your customer seems a bit tight, have to work out which is worse, no drier or leaving one in too long.

    Jon
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Replacing condenser after comp failure

    Quote Originally Posted by comet289 View Post
    i am new to this site and have enjoyed reading the discussions. that being said, i was surprised to see how this question could have these different answers. you always, always change the filter drier every single time you open a system.
    Hi Comet, welcome to RE!

    Its a mini split style system which generally don't have a drier fitted in the line set, as its either an expansion line or a suction that will become a hot gas line in heating mode, there is usually a small filter in the outdoor unit, these systems really rely on good install practices for a long life, though they don't always get it...

    Jon
    Mostly found in Oxfordshire, UK :)

  15. #15
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    Yeah I'll put it to the customer see what they are willing to pay for we can only advise

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Replacing condenser after comp failure

    You simply dont have any filter to change on single split AC system. They are mostly without any drier.

  17. #17
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Replacing condenser after comp failure

    any compressor failure warants a acid test , had a similar situation last week the compressor was down to earth.
    and the oil was a black as the road .
    when fitting the new outdoor unit to the ( iwill call it diry pipework) old indoor and pipework, added a can of acid away .
    have done this a couple of times now and all is ok.
    we are in the process of ordering in some driers to use as a matter of cource in this situation.
    comms rooms with splits are flogged to death imho.
    we fit driers when moisture is suspected also.
    with splits i usualy find the suction line can be frozen back to the service port , the flare nut is a block of ice even when lagged the unit stops , nut defrosts , water tracks down the threads, freezes and so on , till the flare leaks and it get worse .
    i belive that the outdoor runs at a very low presure , something to do with empalthy and the low humidity of the room .
    i am not the best guy to explain this , i only fit the new units , when the others expire. .

  18. #18
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Replacing condenser after comp failure

    Quote Originally Posted by still learning View Post
    any compressor failure warants a acid test , had a similar situation last week the compressor was down to earth.
    and the oil was a black as the road .
    when fitting the new outdoor unit to the ( iwill call it diry pipework) old indoor and pipework, added a can of acid away .
    have done this a couple of times now and all is ok.
    we are in the process of ordering in some driers to use as a matter of cource in this situation.
    comms rooms with splits are flogged to death imho.
    we fit driers when moisture is suspected also.
    with splits i usualy find the suction line can be frozen back to the service port , the flare nut is a block of ice even when lagged the unit stops , nut defrosts , water tracks down the threads, freezes and so on , till the flare leaks and it get worse .
    i belive that the outdoor runs at a very low presure , something to do with empalthy and the low humidity of the room .
    i am not the best guy to explain this , i only fit the new units , when the others expire. .
    Why not just flush the pipe work. Far better solution to remove what's in there rather than trying to mask it by adding chemicals...

  19. #19
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Replacing condenser after comp failure

    Always flush and don't forget to put the seat down after you've finished.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  20. #20
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Replacing condenser after comp failure

    Think acid away needs a drier to work as once its collected to acid it in turn is caught by the drier, not sure what would happen if there isn't one as in jap style ac.
    Mostly found in Oxfordshire, UK :)

  21. #21
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    So what's the best approach should I blow it through with OFN or what's the best flushing agent to use. I will defo do a acid test and depending on the results will advise the customer accordingly

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Replacing condenser after comp failure

    In my opinion, best option is to change outdoor and indoor unit and pipes. Second best option is to install burnout filter and remove it after its job is done.

  23. #23
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    That's what I would do. 9 out 10 cases if I'm replacing the outdoor on a split I replace full system but this job isn't one of our sites we sub contractors so just do as we are told.

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Replacing condenser after comp failure

    Than, just do as you told!

  25. #25
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Replacing condenser after comp failure

    we had some stuff called "endo flush" and a pump to pump it round ( cost a fortune ) the pump stopped pumping and ended up blasting it out( endo flush) with ofn ,
    the pump is still in the workshop to this day , our boffin will look at it one day.
    i just use what i am given , till someone tells me a betterway.
    which i will probably find a better way on this site .

  26. #26
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Replacing condenser after comp failure


  27. #27
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Replacing condenser after comp failure

    Used Endoflush a few times. Found it sits in the saggy pipework and blowing OFN through just skims over the top of it and doesn't get it all out.
    NRS sell 'AK Flush'. This seems to evaporate in the open so I'd imagine of some of it was sitting in the pipework, enough OFN and vaccing would remove it.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  28. #28
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Replacing condenser after comp failure

    wow nettogaz looks good.
    we also had something called "genosalve" at one time( i may of spelt this wrong ).
    i also like the idea of using a oil less reclaim rig as a pump.

  29. #29
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Replacing condenser after comp failure

    Update asked powers that be and they instructed me to just swap outdoor pressure test evacuate and open valves. Probably should of got it in writing. So started job today took old unit out and stop. The new unit sent was wrong one. Try again in a week or so and I'm just gonna do as I'm told.

  30. #30
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Replacing condenser after comp failure

    hope they get you back when it fails again sometime in the future .