    Charge compensator alternative



    Hi,

    does anyone know of alternative to using a charge compensator for heat pumps?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charge compensator alternative

    Correctly sized accumulator?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Charge compensator alternative

    Can your please clarify what is actually a charge compensator.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charge compensator alternative

    Quote Originally Posted by Magoo View Post
    Can your please clarify what is actually a charge compensator.
    I had to do some reading up myself

    Copied from an Emerson bulletin---
    http://www.hvacrinfo.com/cope_ae_bulletins/TAE1331.PDF

    Charge compensator's: Charge compensator's are devices that store excess refrigerant during
    the heating operation of a heat pump with a TXV refrigerant control.

    Unlike an orifice, a TXV will not allow excess refrigerant to flood back to the compressor. This means that the excess system refrigerant will either have to back up in the indoor coil during heating, causing high head pressure, or be stored in a charge compensator until needed.

    A charge compensator is normally a hollow vessel with only one opening that is attached to the vapor line. The shell is usually attached to the outdoor coil or has a line from the outdoor coil running through it for extra cooling during heating and to drive the refrigerant out during A/C operation. Again the size is dependent on how much refrigerant has to be removed from the system throughout the system operating map.

    One point that is often overlooked is that this vessel contains liquid under fairly high pressure during heating. At the beginning of defrost, as the vapor line becomes the suction line leading directly into the compressor, most of the liquid refrigerant from the charge compensator is dumped directly into the compressor shell. Considering many hundreds of defrost cycles, this might have an adverse effect on the compressor.

    A better design would be a charge compensator that can meter refrigerant back to the compressor at an acceptable rate. This design could take the form of a standpipe inside the
    compensator with a small liquid return orifice at its base. A passing criteria for this design would be a compressor bottom shell temperature at least 5°F (2.7°C) warmer than the suction line or saturated suction pressure.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Charge compensator alternative

    Brian.
    I have learned some more today.

    Thanks for the info.

    Grizzly

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Charge compensator alternative

    Thanks Brian, good research and reply