    Mitsubishi VRF Replacement



    Hi Folks

    I have a project to replace serveral Mitsubishi PURY P250 YMF C condensers with the new PURY RP 250 YJM-B condensers.

    But my question is can we reuse the older series indoor units?

    Mitsubishi seem very non-committal of the subject.

    Has anyone got any experience of doing this?

    Regards

    Danny



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi VRF Replacement

    All the replace systems I have commissioned so far have indoor units replaced to match R410a outdoor unit.

    YMF-C was R407c with large glide & lower operating pressure than R410a
    I suspect the indoor unit control stratagy was specific to R407c refrigerant

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi VRF Replacement

    I appreciate the different gases and the perhaps different indoor coils but would it be feasible to change the indoor PCB's to allow the change of gas type? [Just thinking out loud]
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Mitsubishi VRF Replacement

    I wouldn't recommend 407 equipment to run on 410 that's for sure

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi VRF Replacement

    Quote Originally Posted by r.bartlett View Post
    I wouldn't recommend 407 equipment to run on 410 that's for sure
    Fair enough..
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi VRF Replacement

    mitsi mr slim indoors have a spare suction flare nut and it states for 22,407,410 ?? universal- i always swap the complete unit-as any old indoor is gonna have a clogged evap coil

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Mitsubishi VRF Replacement

    Quote Originally Posted by install monkey View Post
    mitsi mr slim indoors have a spare suction flare nut and it states for 22,407,410 ?? universal- i always swap the complete unit-as any old indoor is gonna have a clogged evap coil
    Maybe mismatch in indoor/ outdoor communications, or indoor parts are going to be the next to give trouble. Pinching "Install's" customers, or the other way round?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  8. #8
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    95
    Rep Power
    20

    Re: Mitsubishi VRF Replacement

    Thanks for the responses Gents

    Unfortunatly Mitsubishi have finally stated that the two are not compatable due to comms.

    Richard the project would of course be subject to a strength and pressure test to gauge suitablity for r410a.

    Regards

    Danny