    Is it OK (correct) to pump down mini split system in "Heating mode". Or should I pump down unit only in "Cooling mode"?
    I know, there is button on indoor unit for forced cooling, but...
    Thanks



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Pumping down Mini Split

    If you don't know the answer you should probably not be doing it.
    But with the benifit of doubt.....In cooling!!!!!
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Jan 2012
    Location
    Slovakia
    Age
    40
    Posts
    14
    Rep Power
    0

    Re: Pumping down Mini Split

    Sorry for stupid question. Never did it in heating mode. Just still learning.
    Is it because there is not "enought space" for all refrigerant between compressor and 3way valve? Or any other reason? diagram.jpg

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pumping down Mini Split

    It is because the liquid should be stored in the condenser.

    Close the liquid line valve, run it in cooling and when the suction pressure gets to +1psig, 0.1barg, then switch the unit off and close the suction valve.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Pumping down Mini Split

    Quote Originally Posted by infoseaker View Post
    Sorry for stupid question. Never did it in heating mode. Just still learning.
    Is it because there is not "enought space" for all refrigerant between compressor and 3way valve? Or any other reason? diagram.jpg


    If you are in heating mode and try to pump it down the refrigerant
    will have no where to go to, so the refrigerant needs to be in liquid
    form and the only way to do that is to have the system in cooling mode.
    Then shut the smaller of the two outdoor valves and wait for the system
    to pump all the refrigerant into the correct location (inside the condenser).

    taz

    untitled.JPG

  6. #6
    Join Date
    Nov 2011
    Location
    Australia
    Posts
    1
    Rep Power
    0

    Re: Pumping down Mini Split

    Taz24 has the above diagram is in HEATING mode, instead of Cooling, isn't it? I believe he meant to point out the pumping down cycle need to be done in the cooling mode only. some body check please!

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Pumping down Mini Split

    Quote Originally Posted by gicungchoi View Post
    Taz24 has the above diagram is in HEATING mode, instead of Cooling, isn't it? I believe he meant to point out the pumping down cycle need to be done in the cooling mode only. some body check please!
    I was atempting to show him what he described.

    Yes the drawing I did is in heating mode and my explanation on the drawing
    was regarding the space he would have to pump the refrigerant into.

    He already stated there was not enough space to store the refrigerant and Brian
    has explained how to pump the system down.

    So to avoid confusion....

    To pump down an AC it needs to be running in cooling mode.

    Gauges need to be fitted to the suction (largest) valve. The saturated liquid (smallest)
    valve needs to be wound fully in.

    The refrigerant will be returned to the condenser and stored there, after a short time the
    suction gauge will start to drop. When the suction reaches just above zero the suction (largest)
    valve then needs to be wound fully in also.

    The gauge should continue to read zero which will prove no refrigerant is in the
    pipework or evaporator.

    All the best

    taz

    .

  8. #8
    Join Date
    Jan 2012
    Location
    Slovakia
    Age
    40
    Posts
    14
    Rep Power
    0

    Re: Pumping down Mini Split

    thnaks for answers