Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defrost
At the moment iīm building a diy heat pump - Itīs a compact unit (non split) and at the moment i design the refrigerant circuit for it.
Iīve looked at some manufacturers and they have bypassed the expansion valve and filter drier with a liquid line and check valve.
Does anybody know why?
-
12-02-2012, 04:01 PM #2
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
This is because of one-way TXV and filter drier.
-
12-02-2012, 05:00 PM #3
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
I saw it also with a biflow eev. did something happen when itīs going through the filter drier?
-
12-02-2012, 05:07 PM #4
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
beispiel.jpg
But why they doing it?
Itīs an full biflow eev and biflow filter drier
-
12-02-2012, 06:17 PM #5
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
what is 13? Check valve?
-
12-02-2012, 06:20 PM #6
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
Yes --- Danfoss NVR6 - Check valve
-
12-02-2012, 06:21 PM #7
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
Its from an air water source heat pump
-
12-02-2012, 06:23 PM #8
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
and what is flow direction? Up or down? It opend on cooling or on heating?
-
12-02-2012, 07:53 PM #9
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
open direction is down / cooling (defrost)
-
13-02-2012, 05:11 PM #10
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
If it is reversible unit (I mean it can work in heating and cooling mode), I dont know what is this. If it is heat pump with defrost, I can assume this is like capillary tube in frige, because filter-drier is after EXV. It is too high resistanse for liquid/gas mixture. In your case you dont need it. More important is liquid separator on suction line.
-
14-02-2012, 04:50 PM #11
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
-
14-02-2012, 06:23 PM #12
Re: Heat pump refrigerant circuit - bypass filter drier and liquid receiver in defros
If it is solenoid valve I can guess before defrost warm liquid is pushed to cold coil to start defrost before compressor start to improve defrosting. If u have piping schematic diagram of mentioned heat pump.