    Checking Water Flow Rates though a Chiller



    Hi All

    I need to check if I have the correct water flow rate through a chiller.
    I have a 'binder' point on the flow pipework & return pipework from the chiller so I can put a pressure gauge on each and get a pressure drop through the chiller.
    I know what the pressure drop should be through the chiller at the correct water flow rate.
    So is this the correct or best way of determining the flow rate through the chiller or have I got it wrong. Any help advice would be appreciated

    Thanks



  2. #2
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Checking Water Flow Rates though a Chiller

    Thats correct

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Checking Water Flow Rates though a Chiller

    hi dossat,
    there is a way of telling the flow rate psi x diameter? hey remind me , you guys sedgy

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Checking Water Flow Rates though a Chiller

    You can use the good old fashioned Q = m c dt

    If you know the chiller duty just use Q/(4.18x(t1-t2))

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Checking Water Flow Rates though a Chiller

    York used to print a flow rate/pressure drop graph with the chillers and then tell you not to use it!! I believe you can also use the crane balancing valves if you have access to the balancing tool.

    al
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Checking Water Flow Rates though a Chiller

    Hi Dossat,
    How about if you know the required pressure drop.

    Load your chiller up fully and then see if you can trim the flow with the water off regulating valve.

    Until you get the desired pressure drop.
    On most chillers the >t across the evap would be in low single figures fully loaded.

    If you are achieving 4/5 c with say 1 of 2 comps running you have a poor flow.

    As a rule of thumb I multiply the PSI reading by 7 to get the kpa figure. 30 to 70 kpa diff would usually be acceptable.
    When you start getting into the realms of 2/3 psi diff you have a problem.
    I am just generalizing of course and most manufacturers give you tables to calculate flow and >P in their manuals.
    Grizzly

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Checking Water Flow Rates though a Chiller

    All of the above are good but bear in mind that any fouling of the evaporator will make pressure readings unreliable when compared to the flow rate.
    Brian - Newton Abbot, Devon, UK