reverse cycle water-to-water chiller/ heatpump
Hi everybody
Have anyone operated reverse cycle water-to-water chiller/ heatpump ?? any need any special in operation for them ?
Thanks
-
08-02-2012, 05:04 PM #2
Re: reverse cycle water-to-water chiller/ heatpump
some manufacturers are specialized in this type of chiller. I mean u have to change only water direction, no 4-way valve on ref pipes. But controller must manage outlet chilled water temperature to avoid freezing in both modes, heating and cooling. That's important.
-
09-02-2012, 10:31 PM #3
Re: reverse cycle water-to-water chiller/ heatpump
3-way, 4-way
-
10-02-2012, 07:19 AM #4
Re: reverse cycle water-to-water chiller/ heatpump
Yes, many of them. In Norway and Sweden it's quite common. No specific care is needed. Control is on condenser, and evaporator is only controlled for freezing protection.
-
10-02-2012, 03:11 PM #5
Re: reverse cycle water-to-water chiller/ heatpump
Thanks a lot for the answers. My schematic exactly like the reff three way attachment.
@ AlexG : could you name some manufacturers are specialized in this type of chiller ? I want to check different technical specification.
@All : Have you any documents/recommendation related control multi-chiller plant of this kind chiller especially in control sequence and change-over heating/cooling control ?
-
10-02-2012, 04:08 PM #6
Re: reverse cycle water-to-water chiller/ heatpump
I assume it should be a sealed system due to potential legionella?
Last edited by r.bartlett; 10-02-2012 at 05:37 PM. Reason: fookin spel cheekar
-
10-02-2012, 04:55 PM #7
Re: reverse cycle water-to-water chiller/ heatpump
WTA, check websites of Climaveneta or CIAT. I suppose that Carrier or York make this type of units. What is your e-mail?
-
11-02-2012, 01:01 PM #8
-
11-02-2012, 01:39 PM #9
Re: reverse cycle water-to-water chiller/ heatpump
-
11-02-2012, 05:51 PM #10
Re: reverse cycle water-to-water chiller/ heatpump
wta, why dont u use air-to-water heat pumpes? High humidity?
-
20-02-2012, 02:11 PM #11
Re: reverse cycle water-to-water chiller/ heatpump
Becausa architect and acoustic restriction. dry cooler and water-cooled chiller is only variant