Results 1 to 12 of 12
Thread: fujitsu tech info
06-11-2005, 10:20 PM #1
fujitsu tech info
hi, does any1 have any tech info on fujitsu ie fault codes etc...
or any advise on which direction to go with this...
dnt have the model numbers to hand but from what i can remember, the unit is a split, must be around 10.5 kw i think....i remember they are pre charged to 3kg of r22..if that helps...
error code on remote was e01, 01.
communication error between indoor and outdoor...
there are 2 units running off 1 remote so would it be an idea to check each individual unit at a time ....im guessing yes ?
these units have been running ok for about a year now..
any ideas ?
cheers
07-11-2005, 10:27 PM #2
Re: fujitsu tech info
Give Fuji Technical a ring 0870 521 8218
10-11-2005, 04:47 PM #3
Sorry, meant to post this earlier.
Fujitsu Error Codes
Error code EE:EE displayed instead of clock and unit will stop.
1. If unit is ON then press Start/Stop button to turn it off.
2. Press Set Time (down) and Set Temp/Day (down) buttons together for more than three seconds to start self diagnostic display.
3. Press the buttons in 2 again to end check mode.
E:00 Communication error (indoor unit <-> remote controller)
E:01 Communication error (indoor unit <-> outdoor unit)
E:02 Room temperature sensor open
E:03 Room temperature sensor short circuited
E:04 Indoor heat exchanger temperature sensor open
E:05 Indoor heat exchanger temperature sensor short circuited
E:06 Outdoor heat exchanger temperature sensor open
E:07 Outdoor heat exchanger temperature sensor short circuited
E:08 Power source connection error
E:09 Float switch operated
E:0A Outdoor temperature sensor open
E:0b Outdoor temperature sensor short circuited
E:0C Discharge pipe temperature sensor open
E:0d Discharge pipe temperature sensor short circuited
E:0E Outdoor high pressure abnormal
E:0F Discharge pipe temperature abnormal
E:11 Model abnormal
E:12 Indoor fan abnormal
E:13 Outdoor signal abnormal
E:14 Outdoor EPROM abnormal
10-11-2005, 05:55 PM #4
someone's turned off the first outdoor unit..
cheers
richard
10-11-2005, 08:54 PM #5
Hi Brian
We had a fault this week with a fuji cassette and infra red controller, As the controller only has a one way communication with the unit no fault codes were available. The timer led was flashing on a set frequency and the other two leds were flashing at a slower frequency. Turned out to be a sensor fault.
Do you have any codes for the infra red control units?
15-11-2005, 06:44 PM #6
You can find flashing LED fault codes on the ocean air website
http://www.oceanair.uk.com
Just click on technical then fuij fault codes
note the inverter codes are different from standard units- those rather annoying and difficult to interpret fast flash/ slow flash LED sequences
regards aeb200Last edited by Brian_UK; 15-11-2005 at 10:54 PM. Reason: Double link entry corrected
15-11-2005, 11:00 PM #7
Thanks for the link aeb200, very useful.
BrianBrian - Newton Abbot, Devon, UK
16-11-2005, 09:27 AM #8
Originally Posted by rbartlett
E:01 = indoor outdoor comms
01 = second system as 1st system off the remote is always 00
17-11-2005, 08:39 PM #9
Thanks for the replies - most useful
30-11-2005, 05:46 PM #10
both units were on! never did find out what the problem was...
but i think i can remember some mentioning something about the fact that if it had a pump wired into the indoor board for its power that could cause the fault...
solution was told is = rewire the pump into an external power source such as emergency light etc...
wouldnt think thats very good practice but there you go...
30-11-2005, 08:43 PM #11
01-12-2005, 07:41 PM #12
yes indeed frank, it is a case very much of and
but thats exactly the kind of practise they enforce at that company...iv seen it done with my own eyes
and i bet its nt the only place that does...
your opinons on fujitsu please
By acgibo in forum Air ConditioningReplies: 18Last Post: 26-08-2009, 05:06 PM -
desperately seeking fujitsu
By rbartlett in forum Air ConditioningReplies: 7Last Post: 04-08-2007, 09:06 PM -
Fujitsu
By Abe in forum Air ConditioningReplies: 9Last Post: 21-07-2006, 08:36 AM -
Fuji electric tech info
By Mickvee in forum Air ConditioningReplies: 5Last Post: 04-07-2005, 07:07 PM -
Tech info or direction to for data Mitsubishi RR120 220/240v rotary compressor
By eskimo2 in forum Technical SpeculationsReplies: 4Last Post: 04-01-2005, 04:04 AM